How to backup ACS355 parameters into my laptop?
Hi, I have abb ACS355-03E-07A3-4 drive with an ACS-CP-C Basic Control Panel. I want to make a backup of drive parameters in my laptop. I know the method to download the parameters into the basic control panel but what I want is to directly connect my drive to the laptop and download/upload the parameters.
What I found from my homework is that one can connect ACS355 using OPCA-02 adapter to the laptop and then use DriveWindow Light 2 for the parameter backup and restore. I need confirmation on this?
Also, are there any other methods available to do the same?
Warm Regards,
Voted best answer
Hi,
You are right - for ACS355 parameters handling you will need a DriveWindow Light software and OPCA-02 adapter for the drive.
OPCA-02 is a cable (DB9-RJ45) for RS232 - ask your ABB contact if it is included with the software or not.
You are right - for ACS355 parameters handling you will need a DriveWindow Light software and OPCA-02 adapter for the drive.
OPCA-02 is a cable (DB9-RJ45) for RS232 - ask your ABB contact if it is included with the software or not.
Answers
Hi
In addition to the good explanation of kstoilov, you can use also one Flash Drop unit with Drive PM Sw.
In addition to the good explanation of kstoilov, you can use also one Flash Drop unit with Drive PM Sw.
Add new comment