ACS607-120-4-000B15A05126 Ambient Temp Fault, (temp>125F) But Actual Temperature is 32C as seen in parameter 1.10
Voted best answer
Hi,
I found the description below for your problem in tech catalog and FW manual.
Is the fault disappear after some time of idle drive? If yes, most probably the cooling of control board is not good enough.
I think you should look in RMIO (I/O Control board) where some kind of temperature measurement should be implemented.
- The drive will not start if the ambient temperature is below -5 to 0 ° C or above 73 to 82 ° C (the exact limits vary within the given ranges depending on ACS 600 type).
- I/O Control board temperature is lower than -5...0 ° C or exceeds +73...82 ° C.
by cliffreed Rank: 2057 on 1/8/2019 10:01:09 AM | Like (0) | Report
I have looked in hardware,firmware and circuit diagrams.
I can find no information as to where or which control board the temperature sensing is connected.
cliffreed
by cliffreed Rank: 2057 on 1/8/2019 2:56:17 PM | Like (0) | Report
Hello,
Thank you for your prompt reply.
The fault does not disappear after several hours of power off time..
Comes immediately after power up, I will look into RMIO (I/O Control board) as you suggested.
Thanks,