System Extension Load on system that is UP
Hello!
Can I load a system extension while the system is running (in this case PLC connect) or do I need to stop the 800xA system?
Also do I need to install PLC connect on all nodes? I have installed it on 1 AS as of now.
800xA 5.1 is the version we have.
Thanks in Advance!
/Trinity
Can I load a system extension while the system is running (in this case PLC connect) or do I need to stop the 800xA system?
Also do I need to install PLC connect on all nodes? I have installed it on 1 AS as of now.
800xA 5.1 is the version we have.
Thanks in Advance!
/Trinity
Voted best answer
Hi
You can load system extension while the system is running.
Please install the system extension on all nodes before loading the system extension.
Preferable load the system extension by using Configuration Wizard on AS1.
BR Carsten