800xA Softcontroller Connection Problem
Hi,
I am trying to connect soft controller for 800xA V5.1 but not getting success in doing that. I am using a virtual machine Windows Server 2008 R2 standard and trying to connect through local host with ip address 127.0.0.1:2. Please also see the image file for 800xa version install on this VM. soft controller was not initially install with 800xa, later I installed it by copying setup file of soft controller from some other machine. Please help me to resolve this issue.
Thanks & Best Regards,

I am trying to connect soft controller for 800xA V5.1 but not getting success in doing that. I am using a virtual machine Windows Server 2008 R2 standard and trying to connect through local host with ip address 127.0.0.1:2. Please also see the image file for 800xa version install on this VM. soft controller was not initially install with 800xa, later I installed it by copying setup file of soft controller from some other machine. Please help me to resolve this issue.
Thanks & Best Regards,

Answers
You MUST have a cable connected to the ethernet port (ie a valid and active network connection that RNRP can bind to). Probably 127.0.0.1 does not recognize this.
Probably unrelated, but in the image, the soft controller has not been started...
SoftController is not dependant on RNRP.
SoftController is not dependant on RNRP.
I think issue is because of CIT product mis match
check your ControlBuilder , OPC and Connect having the same version as Soft controller
check your ControlBuilder , OPC and Connect having the same version as Soft controller
Add new comment