IET/CCT 4.1.3 and RED670 ver 2.0.0
We generated SCD file from CCT and exported at CI868, CET and same SCD file at RED670, and there is no error during download.
But there is no communication between RED670 and CET/CI868.
After loading SCD (generated by CCT) at IED, we exported ICD file from RED670 and export at CET then it is communicating between CET and RED670
Is there any version compatibility issue between Relay and CCT?
But there is no communication between RED670 and CET/CI868.
After loading SCD (generated by CCT) at IED, we exported ICD file from RED670 and export at CET then it is communicating between CET and RED670
Is there any version compatibility issue between Relay and CCT?
Answers
Hi,
For communication of CI868 with an IED, you have to do goosing either in CCT or using PCM tool and add goose control blocks.
For communication with CET no goosing is required.
For communication of CI868 with an IED, you have to do goosing either in CCT or using PCM tool and add goose control blocks.
For communication with CET no goosing is required.