Is it possible to show analog output's fuse open/wire break signal on freelance 2016 sp1 system ?
Dear Sir/Madam
I m currently working on freelance 2016 sp1 system and facing problem on showing wire break signal on field side for analog output signal . System is PM902F with S800 I/O's. Please let me know the solution for the same.
Best Regards,
Shashikant Pujari.
I m currently working on freelance 2016 sp1 system and facing problem on showing wire break signal on field side for analog output signal . System is PM902F with S800 I/O's. Please let me know the solution for the same.
Best Regards,
Shashikant Pujari.
Answers
For AO820 for example you would choose the signal range of 4..20mA. Then the alarm should occur automatically in Freelance Operations in case of a wire break. If you have chosen 0..20 mA, the the zero current of a wire break counts as a valid signal and will not create an alarm.