Dual startup sync ended with Errors DIC
Front end xa4.1
Back end Safeguard AC415
We are facing an issue of DIC mismatch sync error.
Following is the message in MMCX
"Dual startup sync ended with Errors DIC"
Checked both side database for any DIC mismatch. Corrected DIC mismatch.
Rebooted Both side controllers one by one.(cleared and rebooted Side A controller and loaded backup of Side A in SideB controller)
Rebooted both controllers simultaneously.
Still the same message "Dual startup sync ended with Errors DIC" in MMCX.
Anybody has faced this issue ?
Answers
How did you correct DIC mismatch ? By deleting or creating more DIC's ?
By deleting be careful not to get 'holes' and DDB is not enough normally, you shall use syst level *FINS 8,xxx DINS in P2 mode
Even the MMCX says DIC you should verify all LF 8 (DI signals)
Henrik Skovsgaard
By deleting be careful not to get 'holes' and DDB is not enough normally, you shall use syst level *FINS 8,xxx DINS in P2 mode
Even the MMCX says DIC you should verify all LF 8 (DI signals)
Henrik Skovsgaard