Extract Alarm Analysis report to MS Excel?
We want The alarms need to be analyzed and data has to be gathered for each alarm.
For analyzing the alarms, we need to export the alarms to excel format.
Want to know
1. how this alarm analysis can be enabled,
2. Does it require any separate licensing (License ID)?
3. Does it require IM or is it possible with Just 800xA System without IM?
4. Will it be possible extract alarm analysis report to MS Excel?
For analyzing the alarms, we need to export the alarms to excel format.
Want to know
1. how this alarm analysis can be enabled,
2. Does it require any separate licensing (License ID)?
3. Does it require IM or is it possible with Just 800xA System without IM?
4. Will it be possible extract alarm analysis report to MS Excel?
Voted best answer
1. how this alarm analysis can be enabled
Alarm analysis can be enabled from system configuration console->system setup->configure system->allocate functions for aspect servers(Make redundant if you have redundant)
Then services will be created in service structure and in Service group->special configuration, configure your settings
Then in any structure usually functional structure->on your object create New object by searching alarm analysis (Note: root object should have your alarm list configured for your analysis) and in alarm analysis aspect category select that root Alarm list and apply and you are done.
2. Does it require any separate licensing (License ID)?
800xA operations->ALARM_MGMT is sufficient
3. Does it require IM or is it possible with Just 800xA System without IM?
Not mandatory,Anything you can use
4. Will it be possible extract alarm analysis report to MS Excel?
C:\Program Files (x86)\ABB 800xA\Base\demo->AlarmAnalysisOLEDSample and follow the instaructions for your excel
Alarm analysis can be enabled from system configuration console->system setup->configure system->allocate functions for aspect servers(Make redundant if you have redundant)
Then services will be created in service structure and in Service group->special configuration, configure your settings
Then in any structure usually functional structure->on your object create New object by searching alarm analysis (Note: root object should have your alarm list configured for your analysis) and in alarm analysis aspect category select that root Alarm list and apply and you are done.
2. Does it require any separate licensing (License ID)?
800xA operations->ALARM_MGMT is sufficient
3. Does it require IM or is it possible with Just 800xA System without IM?
Not mandatory,Anything you can use
4. Will it be possible extract alarm analysis report to MS Excel?
C:\Program Files (x86)\ABB 800xA\Base\demo->AlarmAnalysisOLEDSample and follow the instaructions for your excel
Answers

1. Refer to 3BDS011222-600_C_en_System_800xA_6.0_Configuration.pdf
2. No separate license required for above.3. IM not required
4. Refer above picture.
Other option is to use more sophisticated tool called AlarmInsight which requires separate license and has many functions that go way beyond basic tool inbuilt in 800xA.