How do you activate SNTP in IEC61850 server
Hi
How do you configure SNTP in CET and 800xA for IEC61850?
How do you configure SNTP in CET and 800xA for IEC61850?
Answers
Hi,
The IEC61850 OPC server can act as as SNTP client and server for time synchronisation. When IEC 61850 OPC server is configured for receiving time synch, it updates the OS time of the PC. Enable /Disable SNTP client can do in IEC61850 OPC server object properties.
BR
ATP
The IEC61850 OPC server can act as as SNTP client and server for time synchronisation. When IEC 61850 OPC server is configured for receiving time synch, it updates the OS time of the PC. Enable /Disable SNTP client can do in IEC61850 OPC server object properties.
BR
ATP
- SNTP Client / Server configuration shall be configured in CET Project itself
- In CET - Computer Node - IEC61850 OPC Server - Object properties
- SNTP Client shall be configured by providing SNTP Server IP Address, port Number 123 is default and Time sync Period
Else
- SNTP Slave shall be configured by enabling Time Synchronization server as true
- Then do Update & ReUpload
- In CET - Computer Node - IEC61850 OPC Server - Object properties
- SNTP Client shall be configured by providing SNTP Server IP Address, port Number 123 is default and Time sync Period
Else
- SNTP Slave shall be configured by enabling Time Synchronization server as true
- Then do Update & ReUpload