ACS800 Drive Hand/Auto macro (Ready output fail)
Dear all,
I want to configure an ACS800 drive using Hand/Auto macro. Everything is working well, but I can't get the ready signal from the third output which I had configured it to give me the ready status of the drive!! I'm sure about the voltage source and connections.
Could you please help me to solve the problem?
Thanks a lot
I want to configure an ACS800 drive using Hand/Auto macro. Everything is working well, but I can't get the ready signal from the third output which I had configured it to give me the ready status of the drive!! I'm sure about the voltage source and connections.
Could you please help me to solve the problem?
Thanks a lot
Answers
Hi,
What do you have configured for 14.01?
It should be 14.01 = Ready, and in this case you will have ready at X25:2&3 which is RO1
Please note: Ready to function: Run Enable signal on, no fault. Check if you really have a Ready status - look 3.02 Status word and bit meaning in Table 6 FW Manual
Check also 14.04 and 14.05 for Ton / Tof to RO1
What do you have configured for 14.01?
It should be 14.01 = Ready, and in this case you will have ready at X25:2&3 which is RO1
Please note: Ready to function: Run Enable signal on, no fault. Check if you really have a Ready status - look 3.02 Status word and bit meaning in Table 6 FW Manual
Check also 14.04 and 14.05 for Ton / Tof to RO1
Source: ACS800 FW manual