Has anyone encountered the graphic element of a Mot01 function block with a blue cross through it, with no alarms?

This happens as soon as they reset the bucket or there was a trip. Then you need to disable and enable the function block to get it to work again. The alarm appears in the alarm bar but not on the faceplate.
Does any one know what this blue cross means. Below is all I can find on the different graphic element status.

Answers
Sounds like something is messed up with the Alarm handling for that motor. Most Likely you have a duplicate Motor name. Object names MUST be Unique or the Alarm handler cannot tie the AE message to the correct Object.
Search the Motor Name and rename the offendijng duplicate object.
The cross likely is grey, not blue - IE disabled. Resetting the block is doing the same thing as acknowledging the alarm.
Search the Motor Name and rename the offendijng duplicate object.
The cross likely is grey, not blue - IE disabled. Resetting the block is doing the same thing as acknowledging the alarm.