Update media 6.0.3.2 failed
hi,
I was doing update for 800xA 6.0.3 with 6.0.3.2 package. Distribution went through smoothly but then update freeze to updating System Installer (>5h). I rebooted both nodes and after that when I try to do it again I got information that Media in the selected update package is already part of the system. Everything is working but it is saying that media is at the nodes but I can’t update mediaa. Any ideas?
I was doing update for 800xA 6.0.3 with 6.0.3.2 package. Distribution went through smoothly but then update freeze to updating System Installer (>5h). I rebooted both nodes and after that when I try to do it again I got information that Media in the selected update package is already part of the system. Everything is working but it is saying that media is at the nodes but I can’t update mediaa. Any ideas?
Answers
Hello,
Try this
Once you restart the system.
Run this command "ABB.xA.Core.TaskCenter.Application /update" from "C:\Program Files (x86)\ABB 800xA\Base\bin" using command prompt with admin privileges.
This will start the update process from where it got freezed.
Regards,
Sri
Try this
Once you restart the system.
Run this command "ABB.xA.Core.TaskCenter.Application /update" from "C:\Program Files (x86)\ABB 800xA\Base\bin" using command prompt with admin privileges.
This will start the update process from where it got freezed.
Regards,
Sri
Add new comment