what dose the error mean (process voltage too low Error-)
Hi
I'm working with PM564 ... And on AI523 I have an error....(Error identifier =11)/(Error message=Process voltage too low)/(Remedy=Check process voltage).......
what does it mean؟!
what should i do؟!
Thanks
I'm working with PM564 ... And on AI523 I have an error....(Error identifier =11)/(Error message=Process voltage too low)/(Remedy=Check process voltage).......
what does it mean؟!
what should i do؟!
Thanks
Voted best answer
Hi,
The modules are supplied with a process voltage of 24 VDC.
External power supply is connecting Via the terminals ZP and UP (process voltage 24 VDC). Check these voltages. The external power supply connection is carried out via the UP (+24 VDC) and the ZP (0 VDC) terminals.
Refere 3ADR010121 for more details
Br
ATP
The modules are supplied with a process voltage of 24 VDC.
External power supply is connecting Via the terminals ZP and UP (process voltage 24 VDC). Check these voltages. The external power supply connection is carried out via the UP (+24 VDC) and the ZP (0 VDC) terminals.
Refere 3ADR010121 for more details
Br
ATP