Breaker Command via IEC61850
Hi,
you asked one question that breaker open and close command is in BAD state, Did you have resolved this problem. if yes then please share action that you have performed for this.
you used XCBR for open and closed breaker but i used SWSCEI for open and close breaker and same BAD status found.
Thanks
you asked one question that breaker open and close command is in BAD state, Did you have resolved this problem. if yes then please share action that you have performed for this.
you used XCBR for open and closed breaker but i used SWSCEI for open and close breaker and same BAD status found.
Thanks
Answers
Hi,
The issue has resolved. We have to use Selection On-Off & Operation On-Off from CSWI & not from XCBR.
And about that condition as Bad Status, that is a normal state (until that state is energized). For example, If breaker is Power On for the first time, then In CET u wood be able to see that Selection On, Selection Off, Operation On & Operation Off will be having BAD status when seen in Online diagnostics. However as soon as you force selection On (or operation On) position from Off to On either through faceplate or CET, immediately the condition status will change to GOOD.
Same will happen when you do reverse operation.
The issue has resolved. We have to use Selection On-Off & Operation On-Off from CSWI & not from XCBR.
And about that condition as Bad Status, that is a normal state (until that state is energized). For example, If breaker is Power On for the first time, then In CET u wood be able to see that Selection On, Selection Off, Operation On & Operation Off will be having BAD status when seen in Online diagnostics. However as soon as you force selection On (or operation On) position from Off to On either through faceplate or CET, immediately the condition status will change to GOOD.
Same will happen when you do reverse operation.