Alram Timestamp starting with *
I have a couple of alarms (ACT, RTN) that comes with a star (*) right before the timestamp. There are alarms before and after it with normal timestamp.
*28.10.2018 00:55
Does it mean anything special?
thanks for you help in advance,
Shahab
*28.10.2018 00:55
Does it mean anything special?
thanks for you help in advance,
Shahab
Voted best answer
Hello,
Alarms and Events generated after the Summer-Winter switch, notice the star before the time. As the time is changed 1 hour as per daylight saving, a star before the timestamp indicates that the alarm/event has occurred during the change period.
Answers
Hi,
You have put * on date/Time configuration . So change the date/Time configuration in the alarm event configuration.
Open the alarm list-->Click on view configuration--> Format --> Date/Year Format and Remove the star
BR
ATP
You have put * on date/Time configuration . So change the date/Time configuration in the alarm event configuration.
Open the alarm list-->Click on view configuration--> Format --> Date/Year Format and Remove the star
BR
ATP
Add new comment