OPC client setting required in 800xA system.
What the different settings required to read data into 800xA system over OPC.
Answers
Hello,
If your OPC Client is in the same node as the OPC Server (800xA node), then you can browse and read the OPC data via ProgID: ABB.AfwOpcDaServer.
If your OPC Client is in another machine, then you will need to configure DCOM on OPC Server and OPC Client ends. Refer attached manual; topic: DCOM Security Settings for OPC.
If your OPC Client is in the same node as the OPC Server (800xA node), then you can browse and read the OPC data via ProgID: ABB.AfwOpcDaServer.
If your OPC Client is in another machine, then you will need to configure DCOM on OPC Server and OPC Client ends. Refer attached manual; topic: DCOM Security Settings for OPC.