800xA Time Service Different from Windows Time on the same node
Dear Stefan, good afternoon.
I am setting up DST in a system 800xA 5.0 (WinXP and Server 2003). All windows clocks are on the correct time (non-DST) however, opening "Service Structure > Time > Tab -> Time Difference" in the stations it shows an hour ahead (with DST) Window clock on the same node. Check details on the attached snapshot.
Can you help with that please? Thank you very much in advance
I am setting up DST in a system 800xA 5.0 (WinXP and Server 2003). All windows clocks are on the correct time (non-DST) however, opening "Service Structure > Time > Tab -> Time Difference" in the stations it shows an hour ahead (with DST) Window clock on the same node. Check details on the attached snapshot.
Can you help with that please? Thank you very much in advance
Answers
Never seen before, but looks like conflict in which TZ is in effect.
Have you restarted the workplace since changing Time Zone? Maybe even try giving the AfwTime Service a restart?
Have you restarted the workplace since changing Time Zone? Maybe even try giving the AfwTime Service a restart?
What is the time setting in the control builder. you can see this by Open Tools > Maintenance > Clock Synch > Time Set.
Sharing my experience... it looks like tzedit.exe did not change all windows registries so, OS was looking to the right one but system 800xA to the wrong. Atfer changing Windows registries system 800xA went to right time.
Hello,
Check the following :
1.time sync mechanism followed like GPS-Controller-CS-afw time to other xA nodes recommended for best accuracy for Ac800M (assuming you have).
2.Ensure time zone is followed is common in controller and afw nodes (looks you have time zone issue).