Web Server Profibus - System 6.0
Hi,
How can I configure the web server - Profibus Management (in Internet Explorer).
I have a system 6.0 (update 5.1 Rev B). After the update I can not access the web server.
Thank you for your cooperation.
How can I configure the web server - Profibus Management (in Internet Explorer).
I have a system 6.0 (update 5.1 Rev B). After the update I can not access the web server.
Thank you for your cooperation.
Voted best answer
Hello,
From SV6.0 the WebServer has to be enabled first: In CBM go online, then right-click the PM8xx -> Select “Enable Web Server”.
Default user name is “service” and default password is “ABB800xA”, to start the WebServer.
- Refer Section 6 from the attached manual.