IEC61850 800xA OPC server
Hi
Do you still working with 800xA and relays? Do you have the SCD file on the SEPAM project four years back?
I am knew on using IET600, only used CCT. I have got the SCD from Schneider and have to interface it to the OPC.CID.
Do you still working with 800xA and relays? Do you have the SCD file on the SEPAM project four years back?
I am knew on using IET600, only used CCT. I have got the SCD from Schneider and have to interface it to the OPC.CID.
Answers
Hi Anny
Yes I do. Maybe it is this, but I'm not 100% sure which file you are referring to. There are a lot of projects with SEPAM from 2014.
If you import this into IET600, you can see the things done "on top off" the scd file you receive from Schneider. Inserting conducting equipment if needed in the interface with 800xA, assigning RCB's etc.
If you have any questions with how to use IET600, please let me know.
Yes I do. Maybe it is this, but I'm not 100% sure which file you are referring to. There are a lot of projects with SEPAM from 2014.
If you import this into IET600, you can see the things done "on top off" the scd file you receive from Schneider. Inserting conducting equipment if needed in the interface with 800xA, assigning RCB's etc.
If you have any questions with how to use IET600, please let me know.
Hi
For enabling and disabling of a circuit breaker faceplate. Will you use the CILO?
For enabling and disabling of a circuit breaker faceplate. Will you use the CILO?
Hi
Do you have a screenshoot of the IEDmapping in 800xa for Sepam relay?
Do you have a screenshoot of the IEDmapping in 800xa for Sepam relay?
Add new comment