I add a graphic display aspect in an object at the object type structure and the default aspect become the graphic display instead of the face plate.
So i need to get back the default aspect to the main faceplate.
I tried to click right on the main faceplate aspect and click on details and then aspect view and check on the default aspect box but it wasn't useful. Any solution for this problem?
So i need to get back the default aspect to the main faceplate.
I tried to click right on the main faceplate aspect and click on details and then aspect view and check on the default aspect box but it wasn't useful. Any solution for this problem?
Voted best answer
Answers
Modifying the APL affects EVERY object in the system. So if you change this then you need to understand the impact on everything. Normally, the standard settings on the APL will already make faceplates a higher priority than both VB and PG2 graphics.
In your case it might simply be that the Operator Graphic ALSO has the "Default Aspect" Key set.
Make sure you only have ONE aspect configured to be the default aspect.
In your case it might simply be that the Operator Graphic ALSO has the "Default Aspect" Key set.
Make sure you only have ONE aspect configured to be the default aspect.
Hello,
You can move the built-in key "Default Aspect" to the top of the Precedence List, and then assign the aspect key "Default Aspect" to the aspects required to be default aspects for the objects.

Refer topics: 'Precedence using Aspect Key' and 'How to set the aspect key as Default Aspect' from the attached manual.
You can move the built-in key "Default Aspect" to the top of the Precedence List, and then assign the aspect key "Default Aspect" to the aspects required to be default aspects for the objects.

Refer topics: 'Precedence using Aspect Key' and 'How to set the aspect key as Default Aspect' from the attached manual.