How to send OPC AE to Third party system from xA 5.1 Rv D FP4 System..?
Hello,
How to send OPC AE to Third party system from xA 5.1 Rv D FP4 System..?
can you give the procedure details.
How to send OPC AE to Third party system from xA 5.1 Rv D FP4 System..?
can you give the procedure details.
Answers
Please refer System 5.1 Configuration manual 3BDS011222. Try to search for "Accessing the 800xA OPC Server" section.
If your third party system has OPC AE client you can access alarm and events in ABB 800xA.
As other responds here check manual for dcom setup etc.
As other responds here check manual for dcom setup etc.
Hello,
I don't have a step-by-step document showing the procedure, but you can refer attached manual, page 474 to 476.
You will need to configure DCOM permissions on OPC Server (xA 5.1 FP4 RevD node) and OPC Client (Third Party system).
You can then browse OPC AE tags from ProgID: ABB.OPCEventServer.
I don't have a step-by-step document showing the procedure, but you can refer attached manual, page 474 to 476.
You will need to configure DCOM permissions on OPC Server (xA 5.1 FP4 RevD node) and OPC Client (Third Party system).
You can then browse OPC AE tags from ProgID: ABB.OPCEventServer.