OPC AE smiley becomes red
We have 2 nos of AC800M and 4 nos of HI controller
the problem is OPC AE smiley becomes red after 2 minutes or 5 minutes and it happens only for HI controllers.
AC800M DCS is working fine.
The version is 5.1 Rev E FP4 RU4
sir,Please suggest.
the problem is OPC AE smiley becomes red after 2 minutes or 5 minutes and it happens only for HI controllers.
AC800M DCS is working fine.
The version is 5.1 Rev E FP4 RU4
sir,Please suggest.
Answers
Hello,
I believe this Bulletin (attached) is relevant to the problem you have defined.
Confirm with the sections: Products Concerned and Description.
Correction is defined in section: Corrective Action or Resolution section.
I believe this Bulletin (attached) is relevant to the problem you have defined.
Confirm with the sections: Products Concerned and Description.
Correction is defined in section: Corrective Action or Resolution section.
Add new comment