Converting Engineering Studio Function Designer code to Compact Control Builder format
Hi friends,
Is it possible to convert Engineering Studio Function Designer code (from 800xA) to a Compact Control Builder project format?
Do you have any tips or recommendations?
Thanks fo attention.
Is it possible to convert Engineering Studio Function Designer code (from 800xA) to a Compact Control Builder project format?
Do you have any tips or recommendations?
Thanks fo attention.
Voted best answer
Hello Jean,
Function Designer supports only 800xA and not CHMI.
So, you need to do the following:
1. In your 800xA system, make sure you have Allocated and then Generated all the Function Diagrams having the code, so that all the code is moved to the CBM project.
2. Then Save the CBM project in CCB format, as per the below screenshot.

Function Designer supports only 800xA and not CHMI.
So, you need to do the following:
1. In your 800xA system, make sure you have Allocated and then Generated all the Function Diagrams having the code, so that all the code is moved to the CBM project.
2. Then Save the CBM project in CCB format, as per the below screenshot.