Problem in MB300 Alarm & Event List
Hello,
Problem Description:
After CPU power restart, Alarm & Event list for a particular MB300 node is not working in the MB300 network.
Other Nodes Alarm & Event list are working without any problem.
The same problem was noticed earlier. And, found that RTA node was missing in the Master Table View.
So, manually added the RTA node in the particular CPU and Alarm & Event list is started to work.
This time also found the RTA node was missing in the Master Table view, manually added the RTA node.
but, Alarm & Event list is not working.
I would like to get clarification for,
1. Why the RTA node gets disconnected from the CPU during power restart ?
2. Can we try by removing & Adding back the RTA node which might solve the problem ?
System details :
CPU type - AC 450, PM510
CPU total - 4 nos (2 CPU in each Rack)
attached the screen shot for more details.
appreciate your quick reply.
Regards
Problem Description:
After CPU power restart, Alarm & Event list for a particular MB300 node is not working in the MB300 network.
Other Nodes Alarm & Event list are working without any problem.
The same problem was noticed earlier. And, found that RTA node was missing in the Master Table View.
So, manually added the RTA node in the particular CPU and Alarm & Event list is started to work.
This time also found the RTA node was missing in the Master Table view, manually added the RTA node.
but, Alarm & Event list is not working.
I would like to get clarification for,
1. Why the RTA node gets disconnected from the CPU during power restart ?
2. Can we try by removing & Adding back the RTA node which might solve the problem ?
System details :
CPU type - AC 450, PM510
CPU total - 4 nos (2 CPU in each Rack)
attached the screen shot for more details.
appreciate your quick reply.
Regards
Answers
First of all check your node descriptors on the RTA board(s)... There might be a node descriptor towards this node, that blocks events (property EVENT = 1) from that particular node...
Regs
Stephan
Regs
Stephan
Add new comment