HART CONNECTION PROBLEM WITH AI815


Greetings,
I have two remote IO for using AI815 for HART. For Remote IO 1 I communication with hart temp. trans. But Remote IO 2 I dont have enable communication when I try it. Error is device is not assigned to a channel. Both of them adjust is some. But one is work another dont work. I use same DTM file. Why appear this situation. Best regards.
Answers
Hi there,
Please find attached screenshot from 800xA Device Management configuration manual showing the possible reasons and possible solutions for this error message. Follow the possible reasons and possible solutions to get rid of this error.
Also,
1) Check if proper assignment of CI840s to the proper channel in the fieldbus management aspect of the CI854.
2) Was engineering done without Device Management Profibus/HART software installed? And later the software and extension were installed?
If you are not able to manually resolve it, you can contact your regional support center for sharing the FBBAspectValidator tool and the procedure how to use it, which will rectify this error.
Hope this helps. :)
Please find attached screenshot from 800xA Device Management configuration manual showing the possible reasons and possible solutions for this error message. Follow the possible reasons and possible solutions to get rid of this error.
Also,
1) Check if proper assignment of CI840s to the proper channel in the fieldbus management aspect of the CI854.
2) Was engineering done without Device Management Profibus/HART software installed? And later the software and extension were installed?
If you are not able to manually resolve it, you can contact your regional support center for sharing the FBBAspectValidator tool and the procedure how to use it, which will rectify this error.
Hope this helps. :)