I have 4 no of different pm864 controller I am not able to open web interface for Ci in 1 no of controller through Internet explore. For remaining 3 no of controller it's working fine. Please suggest. Thanks in Advance.
Answers
Check if you have enabled web server. In CBM online mode, right-click the PM8xx --> Select “Enable Web Server”.
1. Check Browser settings are okay as per pre-requisite
2. if your not accessing webserver from Connectivity server ( other CS Node), please ensure TCP/IP forwarding is enabled in RNRP .
3. Please make sure " Automatic Detect settings" is disabled in Network adapter
4. Check whether Controller is reachable from the Node where you are trying to open Webserver
With above requisite, try to clear browser history and start typing Controller IP Address in address bar.
if login window appear, then username = service & password = ac800m (default)
2. if your not accessing webserver from Connectivity server ( other CS Node), please ensure TCP/IP forwarding is enabled in RNRP .
3. Please make sure " Automatic Detect settings" is disabled in Network adapter
4. Check whether Controller is reachable from the Node where you are trying to open Webserver
With above requisite, try to clear browser history and start typing Controller IP Address in address bar.
if login window appear, then username = service & password = ac800m (default)
With SV 5.1 RevB, I believe you are using AC 800M Controller Firmware, Version: 5.1.0/1. There is a known problem with the Web Server for this version. PIN: 800xACON-AD-5101-013. Confirm once.
Refer http://search.abb.com/library/Downloa...
I would also suggest to try restarting the Controller and check the Web Server status.
Refer http://search.abb.com/library/Downloa...
I would also suggest to try restarting the Controller and check the Web Server status.
by U3689 Rank: 557 on 8/29/2018 6:23:30 PM | Like (0) | Report
System Version 800xA 5..1 Rev B