Addition of client on redundant Servers in 800xa Ver 5.1
I have redundant servers and 2 client PC so i want to connect one more pc as a Operator 3 in network. My question is that after normal installation like single engineering node how i can proceed for addition of client and to make a operator workplace for operator 3. Please help.
Thanks in advance.
Software ver - 800xA ver 5. 1
Thanks in advance.
Software ver - 800xA ver 5. 1
Voted best answer
Attached screenshot file for your reference (for installtion of additional operator client using setup package).
Answers
Hi,
You cannot add an single engineering node type installation as a client in a running system.
If you have a running system installed. I suggest you use system planner and make fresh setup package including New operator client.
New operator station (operator3) cannot be installed separately, it has to be in existing network for installation.
After xA installation, you can add client in running system through configuration wizard.
Below screenshot for your reference.

I suggest you to refer 5.1 installation manual.
Thanks
You cannot add an single engineering node type installation as a client in a running system.
If you have a running system installed. I suggest you use system planner and make fresh setup package including New operator client.
New operator station (operator3) cannot be installed separately, it has to be in existing network for installation.
After xA installation, you can add client in running system through configuration wizard.
Below screenshot for your reference.

I suggest you to refer 5.1 installation manual.
Thanks
1.delete the 800xa system that on the single node,
2.set the ip and mask same to the existing system, and connect the new pc into the network correctly,
3.in the existing system, add the new single node into the system by the configuration wizard .
2.set the ip and mask same to the existing system, and connect the new pc into the network correctly,
3.in the existing system, add the new single node into the system by the configuration wizard .
Hello,
I know its kinda late to answer, but this might really help you.
https://forum-controlsystems.abb.com/Document/20199031/800xA-SV-5-1-Automated-I
nstallation-Procedure-For-Beginners
I know its kinda late to answer, but this might really help you.
https://forum-controlsystems.abb.com/Document/20199031/800xA-SV-5-1-Automated-I
nstallation-Procedure-For-Beginners
Add new comment