Hi everyone,
I am to connecting my control builder to the SoftController. For the configuration i added the IP adresse of the SoftcController to the "System Identity" and "Ethenet Settings". when I try to download and go online, I get this error message: "HW Configured controller model does not match connected controller".
Any suggestions to what I could change please?
I am to connecting my control builder to the SoftController. For the configuration i added the IP adresse of the SoftcController to the "System Identity" and "Ethenet Settings". when I try to download and go online, I get this error message: "HW Configured controller model does not match connected controller".
Any suggestions to what I could change please?
Answers
Hi,
Check Soft controller and Control Builder version, should be same.
Also check library connected to controller.
Check Soft controller and Control Builder version, should be same.
Also check library connected to controller.
Please check the below steps are performed
1. Make sure you have started Soft controller
2. Add Soft controller IP like 192.168.x.x:2( if 2 is selected in soft controller ) in OPC Server present in Connectivity server
3. Then Open CBM
4. Enable simulate hardware as per below screenshot
5. Then Controller System identity shall be as same as mentioned in OPC Server
6. Now Right Click over controller -> Properties -> simulate hardware
Then try to download the logic
Greetings,
Have you ever select the "Simulate Hardware" option?
Hope it hleps.
Have you ever select the "Simulate Hardware" option?
Hope it hleps.