SmartClient 800xA Aspect Links
Hello,
A 800xA has in their graphics displays aspect links to show trend displays.
The problem is, when the user is using the SmartClient and open the Graphic display the system is no able to show it because is not supported. Is possible to put a button in the graphic display who works calling trend displays in 800xA and SmartClient?
the image below shows the error who is displayed.
Regards

A 800xA has in their graphics displays aspect links to show trend displays.
The problem is, when the user is using the SmartClient and open the Graphic display the system is no able to show it because is not supported. Is possible to put a button in the graphic display who works calling trend displays in 800xA and SmartClient?
the image below shows the error who is displayed.
Regards

Voted best answer
You are correct in your assumption that Aspect Links & ActiveX components embedded in PG2 Graphics do not translate their use into Smart Client Panels. However, This does not preclude the user from configuring standard button functions in PG2 and having them translate correctly to Smart Client Panels. This thing to remember in this function is that when moving to a standard PG2 Trend Display, there is no way to insert a button onto this type of Display so that the user can return to the original Graphic. Any button configuration on a PG2 Graphic will substitute the original Panel in SC with the new Graphic. One suggestion would be to create a trend display with the PG2 Trend element(s), and also configuring a return button on this Graphic. This particular graphic does not have the button configured, however on other examples available upon request, I can supply these functions.

Which as in this example can be inserted into Smart Client as a PG2 Graphic.

Another method would be to create a set of Tabs in Smart Client representing an area of the Plant that contain all the PG2 & Trend Displays for that area.

I hope this helps.
Regards,
Geof Ledin


Which as in this example can be inserted into Smart Client as a PG2 Graphic.

Another method would be to create a set of Tabs in Smart Client representing an area of the Plant that contain all the PG2 & Trend Displays for that area.


I hope this helps.
Regards,
Geof Ledin