Automation Builder 2.1 can't open "Communication Parameters" box
The older versions of Automation Builder allow serial RS-232 connection to PLC's but I can't find where the option to configure this has gone.
Answers
Hi,
Right Click on CPU then use advanced settings.
Below screenshot and link for your reference:

https://www.youtube.com/watch?v=PL9Ws...
Hope that Helps
Right Click on CPU then use advanced settings.
Below screenshot and link for your reference:

https://www.youtube.com/watch?v=PL9Ws...
Hope that Helps
Hi Matheos
the answer of Dash is right, in doubt about the configuration of Automation Builder, I can suggest one new installation
Hope this help you
the answer of Dash is right, in doubt about the configuration of Automation Builder, I can suggest one new installation
Hope this help you
A few people I know all have the same issue as me as shown. If you install software and the button to click is disappeared then its not an issue of the installation (I've tried this 3 times now). I'm using windows 10 but haven't tested with different OS to see if that might be the problem.
Hi Matheos
your screenshot is referring the Codeys session.
All communication settings must be done in Automation Builder, later when you open Codesys, it inherits the settings from the Automation Builder suite. Follow the advice of Dash or on youtube you can find tutorials for this type of settings
your screenshot is referring the Codeys session.
All communication settings must be done in Automation Builder, later when you open Codesys, it inherits the settings from the Automation Builder suite. Follow the advice of Dash or on youtube you can find tutorials for this type of settings
by romukas009 Rank: 2843 on 3/18/2019 5:21:07 AM | Like (0) | Report
Did you find solution? I have same problem.