Sir, what are the steps to be followed in order to interface 800XA and WinCC HMI. plz help
Answers
What protocol is used /planned for interface ?
Data flow is both direction ?
Data flow is both direction ?
Greetings,
800xA system used OPC protocol for connecting the CPU.
If you want to implement WinCC HMI directly to Connectivity Server, you should use OPC Server/Client architecture.
In other case, if you want to get datas driectly from CPU you have to share , what kind of protocol you prefer to use.
Hope it helps you.
800xA system used OPC protocol for connecting the CPU.
If you want to implement WinCC HMI directly to Connectivity Server, you should use OPC Server/Client architecture.
In other case, if you want to get datas driectly from CPU you have to share , what kind of protocol you prefer to use.
Hope it helps you.
WinCC HMI Shall support OPC ( Client & Server), Modbus TCP/IP, Profibus and so on.
As Project requirement, You shall configure the same in both ends.
Please provide the communication protocol planned. so support shall be more precise
As Project requirement, You shall configure the same in both ends.
Please provide the communication protocol planned. so support shall be more precise
Hi,
It is very easy to implement in 800xA. In your case, xA is client or server?
If xA is a client,
1. DCOM settings : we need to do DCOM settings in server as well as client side.For these settings refer 800xA configuration manual page num:470.
2.User creation: refer page num : 477.
3.once you complete these settings , try to read their tags from your server using third party client simulator like Matrikon (for testing).If not possible, In wincc side you need to do some settings for accessing their tags.
It is very easy to implement in 800xA. In your case, xA is client or server?
If xA is a client,
1. DCOM settings : we need to do DCOM settings in server as well as client side.For these settings refer 800xA configuration manual page num:470.
2.User creation: refer page num : 477.
3.once you complete these settings , try to read their tags from your server using third party client simulator like Matrikon (for testing).If not possible, In wincc side you need to do some settings for accessing their tags.