i am able to browse tags in matrikon, but not able to connect to 3rd party opc server in plc connect .
I have installed matrikon and 800xa plc connect in the same system of 800xa (say abc system). i am able to browse tags in matrikon. we configured plc connect as follows;- installed plc connect softwares and the graphics for it;- created plc connect object in plant explorer;- in configuration of plc generic (given this system(abc system));- create d new object in the controller of this plc client object;- in the scroll down given plcclient then in edit drive given 3rd party opc server ip address,
but it is showing unable to communicate to opc enum,
but in matrikon it works fine,
please tell us a solution
but it is showing unable to communicate to opc enum,
but in matrikon it works fine,
please tell us a solution
Answers
Make sure you have configured the DCOM settings at both the ends (PLC Connect server node and 3rd party node); as Matricon will bypass the DCOM, but PLC Connect won't. If possible, share PLC Connect log files from path: C:\OperateITDataXXX\AdsServer.
Hi,
Check the DCOM settings and user account & password in both ends.
and check the following things also
Check the DCOM settings and user account & password in both ends.
and check the following things also
- Firewall settings
- Bi-directional DCOM settings is required to enable asynch. calls
- Server computer must allow client to login and launch OPC server
- Client computer must allow OPC server to call back to OPC client
- Browsing for remote OPC servers require OPCEnum.exe in server
- OPCEnum.exe require DCOM Remote Access + Launch + Activation
- Defining a dedicated connect account is more secure than Everyone
- The connect account must be granted access with DCOMCNFG.EXE
- A dedicated (preferably non-admin) 800xA user is required as launching identity for the AfwDsOpcSurrogate.1 server
by Govindaraj
Hello bharath16, Avoid posting same question multiple times
-Admin.