Configuration error
Currently we have 2 ABB CPU PM 583 with a CPU terminal base TB511-ETH C1, when power on the plc this one doesnt work on run mode, we changed the CPU terminal base and it is working well, we already checked up the configuration and everything is good. I would like to know if it is a problem of the terminal base or is it something related with configuration. I eally apreciatte your support
Voted best answer
Hi
not every type of terminal base are always compatible...you need to check the P.N. of your TB511 terminal base with the data sheet attached and verify if your cpu is compatible with the terminal base, I had one case where one new cpu was non compatible with one old TB511 so I had to change the TB base.
For example, one P.N. 1SAP111100R0170 is not compatible with a new cpu
Hope this help you, let us know about the results
not every type of terminal base are always compatible...you need to check the P.N. of your TB511 terminal base with the data sheet attached and verify if your cpu is compatible with the terminal base, I had one case where one new cpu was non compatible with one old TB511 so I had to change the TB base.
For example, one P.N. 1SAP111100R0170 is not compatible with a new cpu
Hope this help you, let us know about the results
Answers
Did you check both the CPUs, with the base which you are suspecting as faulty, with same configuration?
If so, then it might be problem of the Terminal base.
If so, then it might be problem of the Terminal base.
Hi
in addition to previous answer, at the follow link the list of obsolete P.N. in AC500 series, referring to the TB terminal base
http://search-ext.abb.com/library/Dow...
Hope this help you
in addition to previous answer, at the follow link the list of obsolete P.N. in AC500 series, referring to the TB terminal base
http://search-ext.abb.com/library/Dow...
Hope this help you