Hi, Everyone
We are trying to bring some analogue values and counters to ABB 800xA system from MiCOM C264
Sorry to bother you with this question but is it possible to connect the protection relay "schneider MiCOM C264" to ABB 800XA through MODBus? If yes how can we do so and if No is there any other solution to do that (through OPC or Ethernet).
We are trying to bring some analogue values and counters to ABB 800xA system from MiCOM C264
Sorry to bother you with this question but is it possible to connect the protection relay "schneider MiCOM C264" to ABB 800XA through MODBus? If yes how can we do so and if No is there any other solution to do that (through OPC or Ethernet).
Answers
Hi,
Which controller you are using along with 800XA. If it is 800M, CI853 module can communicate with Modbus
Which controller you are using along with 800XA. If it is 800M, CI853 module can communicate with Modbus
I assume you have 800xA with no controller.
If only getting modbus signals from protection relay, you can use PLC Connect. If you want to both send/receive via modbus, you can consider using Top Server to convert modbus to OPC then PLC connect/3rd party OPC to get that to 800xA.
If only getting modbus signals from protection relay, you can use PLC Connect. If you want to both send/receive via modbus, you can consider using Top Server to convert modbus to OPC then PLC connect/3rd party OPC to get that to 800xA.