Real Simulation of plc connect signals using matrikon opc
Hello,
Xa5.1 system running with plc connect signals configured to read data from plant guard opc server.
In office setup We don't have plantguard opc server setup shall with matrikon opc simulation software able to simulate all plc connect signals(alarm and value test) without using plantguard opc server software.
Xa5.1 system running with plc connect signals configured to read data from plant guard opc server.
In office setup We don't have plantguard opc server setup shall with matrikon opc simulation software able to simulate all plc connect signals(alarm and value test) without using plantguard opc server software.
Answers
Hi. In a rudimentary way yes you can test the signasl. However all the Data paths have to be changed from the Matrikon Setup to your real Plantgurad OPC paths. If using PLC Connect signals this is not a problem as all the "tags" will be the same. if using the generic OPC connections within Plant Explorer, then this will not work.