Controller Connection to Clientnetwork lost
Hi,
I have a strange Problem on our System. We do not have connection from the Clientnetwork to one Controller.
Facts:
- Controller is working for about three years
- Other 16 Controller do not have this issue
- If i reboot the Controller, I can ping it for 15 times, after that "Request Time out"
- OPC seems to work, no impact to the Production
- I can not see live values in CB on Client
- I can see live values in CB on Connectivity Server
- I can download CB on Client!!
- I can download CB on Connectivity Server
- OPC DA / AE no Problems available
- Hardware and Task on Client CB are red.
What i tried before:
- Rebooting Controller
- RNRP Setting on Controllers, equal like others
- Analyse RNRP
- Test Responsetime (RNRP Fault Tracer) Option 5 --> From CS OK / From Client OK
(RNRP Fault Tracer) Option 2 (get Configuration Parameters and error logs from one node:
On Connectivity Server:
Always "No Connfiguration error", "no System error"
Client:
Sometimes: "Error, no answer"
Sometimes: "No Connfiguration error", "no System error"
Ping:
On Connectivity Server
Max Response Time 40ms
Client:
no reply
I am a little bit confused, is it a Controller Problem (PEC3) or a rnrp Problem. All other Controllers work fine, so it might be a Controller issue!?
Does anybody know something a solution or a better way for analyse?
thx
I have a strange Problem on our System. We do not have connection from the Clientnetwork to one Controller.
Facts:
- Controller is working for about three years
- Other 16 Controller do not have this issue
- If i reboot the Controller, I can ping it for 15 times, after that "Request Time out"
- OPC seems to work, no impact to the Production
- I can not see live values in CB on Client
- I can see live values in CB on Connectivity Server
- I can download CB on Client!!
- I can download CB on Connectivity Server
- OPC DA / AE no Problems available
- Hardware and Task on Client CB are red.
What i tried before:
- Rebooting Controller
- RNRP Setting on Controllers, equal like others
- Analyse RNRP
- Test Responsetime (RNRP Fault Tracer) Option 5 --> From CS OK / From Client OK
(RNRP Fault Tracer) Option 2 (get Configuration Parameters and error logs from one node:
On Connectivity Server:
Always "No Connfiguration error", "no System error"
Client:
Sometimes: "Error, no answer"
Sometimes: "No Connfiguration error", "no System error"
Ping:
On Connectivity Server
Max Response Time 40ms
Client:
no reply
I am a little bit confused, is it a Controller Problem (PEC3) or a rnrp Problem. All other Controllers work fine, so it might be a Controller issue!?
Does anybody know something a solution or a better way for analyse?
thx
Answers
Any change done on the rnrp TCP forwarding in connectivity server
There are several contradictions I cannot explain.
E.g.
- ping is lost, but you can still see OPC data and perform "Test Responsetime"
- download from CBM @ client server network to controller is possible, but no online values are presented.
RNRP is only working by manipulating the IPv4 routing table to assist with reaching beyond your local network; so any test made from the Control Network itself (e.g. from a Connectivity Server towards a controller) would rule out any influence from RNRP as those tests does not involve any routing, only direct access on a common LAN.
A wild guess would be a problem with the ARP cache, e.g. from some kind of ARP flooding, etc. ARP is used to resolve MAC addresses (on Ethernet, communication is made over physical MAC-addresses after resolving them from volatile IP-addresses). If the ARP-table is flushed partially or completely, communication is not possible with those addresses that were removed.
Some additional information may be hidden in the Network Infomation which you can pull using CBM->Remote System --> Controller Analysis -> [Get] Network Information
However, parts of the logfile you attached makes me wonder if PEC has not yet full implementation of network info - "statistics not complete"?
For a controller to be able to send a telegram to a remote node, it's MAC address must be part of the table above (=successfully resolved via ARP). I sense 172.28.80.21 and 22 are the Connectivity Server, which should be able to ping the controller.
However, a complete Network Information should contain more entries. Here is an example from a non-PEC controller running 5.1 firmware.
As you can see, there are routing entries for the Client Server network (172.16.4.0/22) and for a second control network area (172.16.84.0/22). These entries makes it possible to reach nodes on those remote subnets.
I suggest that you report this problem to the PEC support team; they may ask for help from SE if needed.
E.g.
- ping is lost, but you can still see OPC data and perform "Test Responsetime"
- download from CBM @ client server network to controller is possible, but no online values are presented.
RNRP is only working by manipulating the IPv4 routing table to assist with reaching beyond your local network; so any test made from the Control Network itself (e.g. from a Connectivity Server towards a controller) would rule out any influence from RNRP as those tests does not involve any routing, only direct access on a common LAN.
A wild guess would be a problem with the ARP cache, e.g. from some kind of ARP flooding, etc. ARP is used to resolve MAC addresses (on Ethernet, communication is made over physical MAC-addresses after resolving them from volatile IP-addresses). If the ARP-table is flushed partially or completely, communication is not possible with those addresses that were removed.
Some additional information may be hidden in the Network Infomation which you can pull using CBM->Remote System --> Controller Analysis -> [Get] Network Information
However, parts of the logfile you attached makes me wonder if PEC has not yet full implementation of network info - "statistics not complete"?
<PRINTROUTINGTABLE>
...
W 2018-07-19 17:05:01.688 TODO: VxWorks6.8 - statistics not complete
172.28.80.21 at 00:50:56:a7:4c:db on motetsec0
172.28.80.22 at 00:50:56:a7:80:4b on motetsec0
172.28.80.158 at 00:03:2c:00:2d:0e on motetsec0
...
</PRINTROUTINGTABLE>
For a controller to be able to send a telegram to a remote node, it's MAC address must be part of the table above (=successfully resolved via ARP). I sense 172.28.80.21 and 22 are the Connectivity Server, which should be able to ping the controller.
However, a complete Network Information should contain more entries. Here is an example from a non-PEC controller running 5.1 firmware.
INET route table - vr: 0, table: 254
Destination Gateway Flags Use If Metric
127.0.0.0/8 localhost UR 0 lo0 0
localhost localhost UH 3720229lo0 0
172.16.4.0/22 172.17.80.9 UGS 25388 cpm1 0
172.16.80.0/22 172.16.80.106 UC 78 cpm0 0
172.16.80.9 00:05:5d:64:97:9c UHL 3 cpm0 2
172.16.80.17 00:0d:88:52:fe:89 UHL 1156 cpm0 2
172.16.80.19 68:05:ca:33:dd:77 UHL 8785 cpm0 5
172.16.80.21 00:0d:88:52:fe:91 UHL 239 cpm0 2
172.16.80.32 00:15:17:0d:8b:84 UHL 99822 cpm0 2
172.16.80.51 00:1b:21:60:50:6d UHL 11039226cpm0 2
172.16.80.52 00:1b:21:60:4d:65 UHL 324174246cpm0 2
172.16.80.53 00:1b:21:62:86:7b UHL 519 cpm0 5
172.16.80.102 00:00:23:0a:11:98 UHL 11160347cpm0 2
172.16.80.106 172.16.80.106 UH 21 lo0 0
172.16.80.107 00:00:23:0d:1a:4c UHL 41852735cpm0 2
172.16.80.141 00:0c:29:bd:3f:ed UHL 82 cpm0 2
172.16.80.162 00:0c:29:c1:b8:a9 UHL 11221 cpm0 5
172.16.80.163 00:0c:29:75:56:30 UHL 11712 cpm0 5
172.16.84.0/22 172.17.80.9 UGS 0 cpm1 0
172.17.4.0/22 172.17.80.9 UGS 8 cpm1 0
172.17.80.0/22 172.17.80.106 UC 1459 cpm1 0
172.17.80.9 00:05:5d:64:97:9d UHL 40515 cpm1 5
172.17.80.17 00:0d:88:52:fe:88 UHL 230 cpm1 2
172.17.80.53 00:1b:21:62:86:7a UHL 93 cpm1 5
172.17.80.106 172.17.80.106 UH 0 lo0 0
172.17.80.141 00:0c:29:bd:3f:01 UHL 6 cpm1 5
172.17.84.0/22 172.17.80.9 UGS 0 cpm1 0
ARP:
172.16.80.9 at 00:05:5d:64:97:9c on cpm0
172.16.80.17 at 00:0d:88:52:fe:89 on cpm0
172.16.80.19 at 68:05:ca:33:dd:77 on cpm0
172.16.80.21 at 00:0d:88:52:fe:91 on cpm0
172.16.80.32 at 00:15:17:0d:8b:84 on cpm0
172.16.80.51 at 00:1b:21:60:50:6d on cpm0
172.16.80.52 at 00:1b:21:60:4d:65 on cpm0
172.16.80.53 at 00:1b:21:62:86:7b on cpm0
172.16.80.102 at 00:00:23:0a:11:98 on cpm0
172.16.80.107 at 00:00:23:0d:1a:4c on cpm0
172.16.80.141 at 00:0c:29:bd:3f:ed on cpm0
172.16.80.162 at 00:0c:29:c1:b8:a9 on cpm0
172.16.80.163 at 00:0c:29:75:56:30 on cpm0
172.17.80.9 at 00:05:5d:64:97:9d on cpm1
172.17.80.17 at 00:0d:88:52:fe:88 on cpm1
172.17.80.53 at 00:1b:21:62:86:7a on cpm1
172.17.80.141 at 00:0c:29:bd:3f:01 on cpm1
As you can see, there are routing entries for the Client Server network (172.16.4.0/22) and for a second control network area (172.16.84.0/22). These entries makes it possible to reach nodes on those remote subnets.
I suggest that you report this problem to the PEC support team; they may ask for help from SE if needed.
by Stefan Stromqvist
Controller log?
by ahuerlimann Rank: 289 on 7/19/2018 10:19:04 PM | Like (0) | Report
##########################
=== Latest startup-log ===
##########################
domain
I 2018-07-11 15:34:30.218 AE System events to controller log: Medium Severity
I 2018-07-11 15:34:30.709 6356 config: PhResp. running... 2 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-11 15:34:30.745 1942 CPhCI854Base::Configure 2 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
I 2018-07-11 15:34:30.995 2654 General: Config succeeded 2 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
I 2018-07-11 15:34:31.169 New I/O-connections configuration.
I 2018-07-11 15:34:31.203 I/O-connections configured.
E 2018-07-11 15:35:09.550 On Unit= 2.30 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-11 15:35:09.550 On Unit= 2.30.1 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-11 15:35:09.550 On Unit= 2.30.2 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
W 2018-07-11 15:35:14.619 A/E Burst: Prevented 5 alarms & events from being printed in the log, refer to an OPC AE client for more info.
I 2018-07-11 15:36:07.348 Create controller configuration domain
I 2018-07-11 15:36:09.349 AE System events to controller log: Medium Severity
I 2018-07-11 15:36:09.950 6356 config: PhResp. running... 2 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-11 15:36:09.969 1942 CPhCI854Base::Configure 2 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
I 2018-07-11 15:36:10.247 2654 General: Config succeeded 2 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
I 2018-07-11 15:36:10.296 New I/O-connections configuration.
I 2018-07-11 15:36:10.308 I/O-connections configured.
E 2018-07-11 15:36:19.747 On Unit= 2.30 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-11 15:36:19.747 On Unit= 2.30 HWError CT0018 0000 See HWTree Error 16#00020001 16#00000008
I 2018-07-11 15:41:56.651 Create applications definition domain
I 2018-07-11 15:41:56.802 Create controller configuration domain
I 2018-07-11 15:41:59.374 New I/O-connections configuration.
I 2018-07-11 15:41:59.808 I/O-connections configuration waiting for application/s.
I 2018-07-11 15:42:00.353 Create application instance domain: R551922203Level1_Co18
I 2018-07-11 15:42:12.453 Create application R551922203Level1_Co18
I 2018-07-11 15:42:14.975 Stop and restart application R479761265Level1_Co18 as R551922203Level1_Co18
I 2018-07-11 15:42:15.250 I/O-connections configured.
I 2018-07-11 16:44:15.093 Create applications definition domain
I 2018-07-11 16:44:15.916 Create controller configuration domain
I 2018-07-11 16:44:18.716 New I/O-connections configuration.
I 2018-07-11 16:44:19.265 I/O-connections configuration waiting for application/s.
I 2018-07-11 16:44:19.754 Create application instance domain: R220068168Level1_Co18
I 2018-07-11 16:44:30.916 Create application R220068168Level1_Co18
I 2018-07-11 16:44:33.617 Stop and restart application R551922203Level1_Co18 as R220068168Level1_Co18
I 2018-07-11 16:44:33.840 I/O-connections configured.
I 2018-07-12 08:33:37.524 Create applications definition domain
I 2018-07-12 08:33:38.273 Create controller configuration domain
I 2018-07-12 08:33:41.023 New I/O-connections configuration.
I 2018-07-12 08:33:41.676 I/O-connections configuration waiting for application/s.
I 2018-07-12 08:33:42.147 Create application instance domain: R154937598Level1_Co18
I 2018-07-12 08:33:53.527 Create application R154937598Level1_Co18
I 2018-07-12 08:33:56.046 Stop and restart application R220068168Level1_Co18 as R154937598Level1_Co18
I 2018-07-12 08:33:56.339 I/O-connections configured.
I 2018-07-12 11:00:27.466 Create applications definition domain
I 2018-07-12 11:00:27.722 Create controller configuration domain
I 2018-07-12 11:00:30.233 New I/O-connections configuration.
I 2018-07-12 11:00:30.869 I/O-connections configuration waiting for application/s.
I 2018-07-12 11:00:31.266 Create application instance domain: R323199388Level1_Co18
I 2018-07-12 11:00:42.225 Create application R323199388Level1_Co18
I 2018-07-12 11:00:44.787 Stop and restart application R154937598Level1_Co18 as R323199388Level1_Co18
I 2018-07-12 11:00:45.037 I/O-connections configured.
I 2018-07-12 11:16:42.022 Create applications definition domain
I 2018-07-12 11:16:42.573 Create controller configuration domain
I 2018-07-12 11:16:45.333 New I/O-connections configuration.
I 2018-07-12 11:16:45.773 I/O-connections configuration waiting for application/s.
I 2018-07-12 11:16:46.224 Create application instance domain: R439626242Level1_Co18
I 2018-07-12 11:16:57.672 Create application R439626242Level1_Co18
I 2018-07-12 11:17:00.273 Stop and restart application R323199388Level1_Co18 as R439626242Level1_Co18
I 2018-07-12 11:17:00.544 I/O-connections configured.
I 2018-07-12 11:40:32.975 Create applications definition domain
I 2018-07-12 11:40:33.398 Create controller configuration domain
I 2018-07-12 11:40:35.926 New I/O-connections configuration.
I 2018-07-12 11:40:36.335 I/O-connections configuration waiting for application/s.
I 2018-07-12 11:40:36.897 Create application instance domain: R456770118Level1_Co18
I 2018-07-12 11:40:47.877 Create application R456770118Level1_Co18
I 2018-07-12 11:40:50.445 Stop and restart application R439626242Level1_Co18 as R456770118Level1_Co18
I 2018-07-12 11:40:50.745 I/O-connections configured.
I 2018-07-12 12:32:43.538 Create applications definition domain
I 2018-07-12 12:32:43.772 Create controller configuration domain
I 2018-07-12 12:32:46.238 New I/O-connections configuration.
I 2018-07-12 12:32:46.785 I/O-connections configuration waiting for application/s.
I 2018-07-12 12:32:47.241 Create application instance domain: R382492436Level1_Co18
I 2018-07-12 12:32:58.339 Create application R382492436Level1_Co18
I 2018-07-12 12:33:01.067 Stop and restart application R456770118Level1_Co18 as R382492436Level1_Co18
I 2018-07-12 12:33:01.422 I/O-connections configured.
I 2018-07-12 12:49:39.450 Create applications definition domain
I 2018-07-12 12:49:41.029 Create controller configuration domain
I 2018-07-12 12:49:43.777 New I/O-connections configuration.
I 2018-07-12 12:49:44.329 I/O-connections configuration waiting for application/s.
I 2018-07-12 12:49:44.752 Create application instance domain: R310448008Level1_Co18
I 2018-07-12 12:49:56.150 Create application R310448008Level1_Co18
I 2018-07-12 12:49:58.783 Stop and restart application R382492436Level1_Co18 as R310448008Level1_Co18
I 2018-07-12 12:49:58.996 I/O-connections configured.
I 2018-07-12 15:48:59.736 Create applications definition domain
I 2018-07-12 15:49:00.552 Create controller configuration domain
I 2018-07-12 15:49:03.501 New I/O-connections configuration.
I 2018-07-12 15:49:03.935 I/O-connections configuration waiting for application/s.
I 2018-07-12 15:49:04.378 Create application instance domain: R390457252Level1_Co18
I 2018-07-12 15:49:15.778 Create application R390457252Level1_Co18
I 2018-07-12 15:49:18.434 Stop and restart application R310448008Level1_Co18 as R390457252Level1_Co18
I 2018-07-12 15:49:18.694 I/O-connections configured.
I 2018-07-13 15:48:22.641 Create applications definition domain
I 2018-07-13 15:48:23.241 Create controller configuration domain
I 2018-07-13 15:48:25.913 New I/O-connections configuration.
I 2018-07-13 15:48:26.462 I/O-connections configuration waiting for application/s.
I 2018-07-13 15:48:27.215 Create application instance domain: R377894541Level1_Co18
I 2018-07-13 15:48:38.550 Create application R377894541Level1_Co18
I 2018-07-13 15:48:41.146 Stop and restart application R390457252Level1_Co18 as R377894541Level1_Co18
I 2018-07-13 15:48:41.560 I/O-connections configured.
I 2018-07-19 14:46:41.811 Create applications definition domain
I 2018-07-19 14:46:43.666 Create controller configuration domain
I 2018-07-19 14:46:46.460 New I/O-connections configuration.
I 2018-07-19 14:46:46.925 I/O-connections configuration waiting for application/s.
I 2018-07-19 14:46:47.385 Create application instance domain: R491531568Level1_Co18
I 2018-07-19 14:47:00.187 Create application R491531568Level1_Co18
I 2018-07-19 14:47:02.715 Stop and restart application R377894541Level1_Co18 as R491531568Level1_Co18
I 2018-07-19 14:47:03.111 I/O-connections configured.
I 2018-07-19 15:05:42.487 Create applications definition domain
I 2018-07-19 15:05:44.049 Create controller configuration domain
I 2018-07-19 15:05:46.705 New I/O-connections configuration.
I 2018-07-19 15:05:47.334 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:05:47.734 Create application instance domain: R165766667Level1_Co18
I 2018-07-19 15:05:59.583 Create application R165766667Level1_Co18
I 2018-07-19 15:06:02.106 Stop and restart application R491531568Level1_Co18 as R165766667Level1_Co18
I 2018-07-19 15:06:02.353 I/O-connections configured.
I 2018-07-19 15:08:02.083 Create applications definition domain
I 2018-07-19 15:08:03.685 Create controller configuration domain
I 2018-07-19 15:08:06.305 New I/O-connections configuration.
I 2018-07-19 15:08:06.855 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:08:07.307 Create application instance domain: R580012655Level1_Co18
I 2018-07-19 15:08:18.985 Create application R580012655Level1_Co18
I 2018-07-19 15:08:21.534 Stop and restart application R165766667Level1_Co18 as R580012655Level1_Co18
I 2018-07-19 15:08:21.752 I/O-connections configured.
I 2018-07-19 15:20:40.089 Create applications definition domain
I 2018-07-19 15:20:41.707 Create controller configuration domain
I 2018-07-19 15:20:44.385 New I/O-connections configuration.
I 2018-07-19 15:20:44.952 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:20:45.388 Create application instance domain: R829075118Level1_Co18
I 2018-07-19 15:20:58.207 Create application R829075118Level1_Co18
I 2018-07-19 15:21:00.735 Stop and restart application R580012655Level1_Co18 as R829075118Level1_Co18
I 2018-07-19 15:21:01.032 I/O-connections configured.
I 2018-07-19 15:24:07.109 Create applications definition domain
I 2018-07-19 15:24:08.587 Create controller configuration domain
I 2018-07-19 15:24:11.409 New I/O-connections configuration.
I 2018-07-19 15:24:11.855 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:24:12.338 Create application instance domain: R450333283Level1_Co18
I 2018-07-19 15:24:24.087 Create application R450333283Level1_Co18
I 2018-07-19 15:24:26.687 Stop and restart application R829075118Level1_Co18 as R450333283Level1_Co18
I 2018-07-19 15:24:27.084 I/O-connections configured.
I 2018-07-19 15:27:06.803 Create applications definition domain
I 2018-07-19 15:27:08.431 Create controller configuration domain
I 2018-07-19 15:27:11.103 New I/O-connections configuration.
I 2018-07-19 15:27:11.652 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:27:12.105 Create application instance domain: R778008856Level1_Co18
I 2018-07-19 15:27:23.981 Create application R778008856Level1_Co18
I 2018-07-19 15:27:26.532 Stop and restart application R450333283Level1_Co18 as R778008856Level1_Co18
I 2018-07-19 15:27:26.796 I/O-connections configured.
I 2018-07-19 15:48:19.455 Create applications definition domain
I 2018-07-19 15:48:20.207 Create controller configuration domain
I 2018-07-19 15:48:22.962 New I/O-connections configuration.
I 2018-07-19 15:48:23.506 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:48:23.929 Create application instance domain: R825167704Level1_Co18
I 2018-07-19 15:48:35.507 Create application R825167704Level1_Co18
I 2018-07-19 15:48:38.106 Stop and restart application R778008856Level1_Co18 as R825167704Level1_Co18
I 2018-07-19 15:48:38.410 I/O-connections configured.
I 2018-07-19 15:49:52.407 Create applications definition domain
I 2018-07-19 15:49:53.008 Create controller configuration domain
I 2018-07-19 15:49:55.776 New I/O-connections configuration.
I 2018-07-19 15:49:56.308 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:49:56.709 Create application instance domain: R825915901Level1_Co18
I 2018-07-19 15:50:08.408 Create application R825915901Level1_Co18
I 2018-07-19 15:50:10.959 Stop and restart application R825167704Level1_Co18 as R825915901Level1_Co18
I 2018-07-19 15:50:11.225 I/O-connections configured.
Start ErrorLog
Autorestart is disabled
Initialized. No time data available.
System time quality: BAD
I 1979-12-31 00:00:01.196 Network Interface 172.28.80.168 (255.255.252.0 ) : 00-03-2c-05-14-61
I 2018-07-19 14:21:06.263 Network Interface 172.29.80.168 (255.255.252.0 ) : 00-03-2c-05-14-62
I 2018-07-19 14:21:06.263 Network Interface 10.41.246.72 (255.255.255.0 ) : 00-03-2c-05-14-63
I 2018-07-19 14:21:06.265
I 2018-07-19 14:21:06.265
I 2018-07-19 14:21:06.266 Product : AC 800PEC PPE100/101
I 2018-07-19 14:21:06.266 Version : 5.1.0/0 (Build 5.1.48.40)
(XF801 integration version: 1.0-0)
I 2018-07-19 14:21:06.266 Created : 2016-12-16
NOTE : This is a BU IS specific firmware. Contact 'hotrollingmillsupport@se.abb.com' for XF801 related support.
I 2018-07-19 14:21:06.267 ABB AB
I 2018-07-19 14:21:06.267
I 2018-07-19 14:21:06.267 Controller Reset
I 2018-07-19 14:21:06.354 Position Module Firmware Name Date Version
I 2018-07-19 14:21:06.355 0 PEC800 FWPEC 2016-12-16 5.1.48.40
I 2018-07-19 14:21:06.355 OMEGA 2016-12-16 5.1.48.40
I 2018-07-19 14:21:06.356 PECIO omega driver 2005-04-13 2.00
I 2018-07-19 14:21:06.356 VICIdrvSim 2012-05-24 7.12
I 2018-07-19 14:21:06.357 CEX simulation N/A 0.0.0.1
I 2018-07-19 14:21:06.357 1 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 2018-07-19 14:21:06.358 FWCI854 PROG 3611540 A 2011-11-10 05.62
I 2018-07-19 14:21:06.358 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 2018-07-19 14:21:06.359 CI-Unit N/A CI854A PR:L
I 2018-07-19 14:21:06.359 2 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 2018-07-19 14:21:06.360 FWCI854 PROG 3611540 A 2011-11-10 05.62
I 2018-07-19 14:21:06.360 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 2018-07-19 14:21:06.361 CI-Unit N/A CI854A PR:J
I 2018-07-19 14:21:06.361 3 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 2018-07-19 14:21:06.362 FWCI854 PROG 3611540 A 2011-11-10 05.62
I 2018-07-19 14:21:06.362 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 2018-07-19 14:21:06.363 CI-Unit N/A CI854A PR:J
I 2018-07-19 14:21:06.363 4 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 2018-07-19 14:21:06.364 FWCI854 PROG 3611540 A 2011-11-10 05.62
I 2018-07-19 14:21:06.364 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 2018-07-19 14:21:06.365 CI-Unit N/A CI854A PR:L
I 2018-07-19 14:21:06.365
I 2018-07-19 14:21:06.366 Actual heapsize: 910708 kBytes, Available heap: 882387 kBytes
I 2018-07-19 14:21:06.384 RunMode
I 2018-07-19 14:21:06.388 License Manager: Feature Name Control_Software
I 2018-07-19 14:21:06.389 License Manager: Version 5.1.0
I 2018-07-19 14:21:06.389 License Manager: Hardware ID 00-00-00-00-00-00
I 2018-07-19 14:21:06.392 System Initialized.
W 2018-07-19 14:21:06.392 Unit= _SWFirmware 172.28.80.168 1040 BUM No conf image found on BUM
##############################################
=== Log fetched at 2018-07-20 07:12:26.016 ===
##############################################
:30.233 New I/O-connections configuration.
I 2018-07-12 11:00:30.869 I/O-connections configuration waiting for application/s.
I 2018-07-12 11:00:31.266 Create application instance domain: R323199388Level1_Co18
I 2018-07-12 11:00:42.225 Create application R323199388Level1_Co18
I 2018-07-12 11:00:44.787 Stop and restart application R154937598Level1_Co18 as R323199388Level1_Co18
I 2018-07-12 11:00:45.037 I/O-connections configured.
I 2018-07-12 11:16:42.022 Create applications definition domain
I 2018-07-12 11:16:42.573 Create controller configuration domain
I 2018-07-12 11:16:45.333 New I/O-connections configuration.
I 2018-07-12 11:16:45.773 I/O-connections configuration waiting for application/s.
I 2018-07-12 11:16:46.224 Create application instance domain: R439626242Level1_Co18
I 2018-07-12 11:16:57.672 Create application R439626242Level1_Co18
I 2018-07-12 11:17:00.273 Stop and restart application R323199388Level1_Co18 as R439626242Level1_Co18
I 2018-07-12 11:17:00.544 I/O-connections configured.
I 2018-07-12 11:40:32.975 Create applications definition domain
I 2018-07-12 11:40:33.398 Create controller configuration domain
I 2018-07-12 11:40:35.926 New I/O-connections configuration.
I 2018-07-12 11:40:36.335 I/O-connections configuration waiting for application/s.
I 2018-07-12 11:40:36.897 Create application instance domain: R456770118Level1_Co18
I 2018-07-12 11:40:47.877 Create application R456770118Level1_Co18
I 2018-07-12 11:40:50.445 Stop and restart application R439626242Level1_Co18 as R456770118Level1_Co18
I 2018-07-12 11:40:50.745 I/O-connections configured.
I 2018-07-12 12:32:43.538 Create applications definition domain
I 2018-07-12 12:32:43.772 Create controller configuration domain
I 2018-07-12 12:32:46.238 New I/O-connections configuration.
I 2018-07-12 12:32:46.785 I/O-connections configuration waiting for application/s.
I 2018-07-12 12:32:47.241 Create application instance domain: R382492436Level1_Co18
I 2018-07-12 12:32:58.339 Create application R382492436Level1_Co18
I 2018-07-12 12:33:01.067 Stop and restart application R456770118Level1_Co18 as R382492436Level1_Co18
I 2018-07-12 12:33:01.422 I/O-connections configured.
I 2018-07-12 12:49:39.450 Create applications definition domain
I 2018-07-12 12:49:41.029 Create controller configuration domain
I 2018-07-12 12:49:43.777 New I/O-connections configuration.
I 2018-07-12 12:49:44.329 I/O-connections configuration waiting for application/s.
I 2018-07-12 12:49:44.752 Create application instance domain: R310448008Level1_Co18
I 2018-07-12 12:49:56.150 Create application R310448008Level1_Co18
I 2018-07-12 12:49:58.783 Stop and restart application R382492436Level1_Co18 as R310448008Level1_Co18
I 2018-07-12 12:49:58.996 I/O-connections configured.
I 2018-07-12 15:48:59.736 Create applications definition domain
I 2018-07-12 15:49:00.552 Create controller configuration domain
I 2018-07-12 15:49:03.501 New I/O-connections configuration.
I 2018-07-12 15:49:03.935 I/O-connections configuration waiting for application/s.
I 2018-07-12 15:49:04.378 Create application instance domain: R390457252Level1_Co18
I 2018-07-12 15:49:15.778 Create application R390457252Level1_Co18
I 2018-07-12 15:49:18.434 Stop and restart application R310448008Level1_Co18 as R390457252Level1_Co18
I 2018-07-12 15:49:18.694 I/O-connections configured.
I 2018-07-13 15:48:22.641 Create applications definition domain
I 2018-07-13 15:48:23.241 Create controller configuration domain
I 2018-07-13 15:48:25.913 New I/O-connections configuration.
I 2018-07-13 15:48:26.462 I/O-connections configuration waiting for application/s.
I 2018-07-13 15:48:27.215 Create application instance domain: R377894541Level1_Co18
I 2018-07-13 15:48:38.550 Create application R377894541Level1_Co18
I 2018-07-13 15:48:41.146 Stop and restart application R390457252Level1_Co18 as R377894541Level1_Co18
I 2018-07-13 15:48:41.560 I/O-connections configured.
I 2018-07-19 14:46:41.811 Create applications definition domain
I 2018-07-19 14:46:43.666 Create controller configuration domain
I 2018-07-19 14:46:46.460 New I/O-connections configuration.
I 2018-07-19 14:46:46.925 I/O-connections configuration waiting for application/s.
I 2018-07-19 14:46:47.385 Create application instance domain: R491531568Level1_Co18
I 2018-07-19 14:47:00.187 Create application R491531568Level1_Co18
I 2018-07-19 14:47:02.715 Stop and restart application R377894541Level1_Co18 as R491531568Level1_Co18
I 2018-07-19 14:47:03.111 I/O-connections configured.
I 2018-07-19 15:05:42.487 Create applications definition domain
I 2018-07-19 15:05:44.049 Create controller configuration domain
I 2018-07-19 15:05:46.705 New I/O-connections configuration.
I 2018-07-19 15:05:47.334 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:05:47.734 Create application instance domain: R165766667Level1_Co18
I 2018-07-19 15:05:59.583 Create application R165766667Level1_Co18
I 2018-07-19 15:06:02.106 Stop and restart application R491531568Level1_Co18 as R165766667Level1_Co18
I 2018-07-19 15:06:02.353 I/O-connections configured.
I 2018-07-19 15:08:02.083 Create applications definition domain
I 2018-07-19 15:08:03.685 Create controller configuration domain
I 2018-07-19 15:08:06.305 New I/O-connections configuration.
I 2018-07-19 15:08:06.855 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:08:07.307 Create application instance domain: R580012655Level1_Co18
I 2018-07-19 15:08:18.985 Create application R580012655Level1_Co18
I 2018-07-19 15:08:21.534 Stop and restart application R165766667Level1_Co18 as R580012655Level1_Co18
I 2018-07-19 15:08:21.752 I/O-connections configured.
I 2018-07-19 15:20:40.089 Create applications definition domain
I 2018-07-19 15:20:41.707 Create controller configuration domain
I 2018-07-19 15:20:44.385 New I/O-connections configuration.
I 2018-07-19 15:20:44.952 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:20:45.388 Create application instance domain: R829075118Level1_Co18
I 2018-07-19 15:20:58.207 Create application R829075118Level1_Co18
I 2018-07-19 15:21:00.735 Stop and restart application R580012655Level1_Co18 as R829075118Level1_Co18
I 2018-07-19 15:21:01.032 I/O-connections configured.
I 2018-07-19 15:24:07.109 Create applications definition domain
I 2018-07-19 15:24:08.587 Create controller configuration domain
I 2018-07-19 15:24:11.409 New I/O-connections configuration.
I 2018-07-19 15:24:11.855 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:24:12.338 Create application instance domain: R450333283Level1_Co18
I 2018-07-19 15:24:24.087 Create application R450333283Level1_Co18
I 2018-07-19 15:24:26.687 Stop and restart application R829075118Level1_Co18 as R450333283Level1_Co18
I 2018-07-19 15:24:27.084 I/O-connections configured.
I 2018-07-19 15:27:06.803 Create applications definition domain
I 2018-07-19 15:27:08.431 Create controller configuration domain
I 2018-07-19 15:27:11.103 New I/O-connections configuration.
I 2018-07-19 15:27:11.652 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:27:12.105 Create application instance domain: R778008856Level1_Co18
I 2018-07-19 15:27:23.981 Create application R778008856Level1_Co18
I 2018-07-19 15:27:26.532 Stop and restart application R450333283Level1_Co18 as R778008856Level1_Co18
I 2018-07-19 15:27:26.796 I/O-connections configured.
I 2018-07-19 15:48:19.455 Create applications definition domain
I 2018-07-19 15:48:20.207 Create controller configuration domain
I 2018-07-19 15:48:22.962 New I/O-connections configuration.
I 2018-07-19 15:48:23.506 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:48:23.929 Create application instance domain: R825167704Level1_Co18
I 2018-07-19 15:48:35.507 Create application R825167704Level1_Co18
I 2018-07-19 15:48:38.106 Stop and restart application R778008856Level1_Co18 as R825167704Level1_Co18
I 2018-07-19 15:48:38.410 I/O-connections configured.
I 2018-07-19 15:49:52.407 Create applications definition domain
I 2018-07-19 15:49:53.008 Create controller configuration domain
I 2018-07-19 15:49:55.776 New I/O-connections configuration.
I 2018-07-19 15:49:56.308 I/O-connections configuration waiting for application/s.
I 2018-07-19 15:49:56.709 Create application instance domain: R825915901Level1_Co18
I 2018-07-19 15:50:08.408 Create application R825915901Level1_Co18
I 2018-07-19 15:50:10.959 Stop and restart application R825167704Level1_Co18 as R825915901Level1_Co18
I 2018-07-19 15:50:11.225 I/O-connections configured.
Start ErrorLog
Autorestart is disabled
Initialized. No time data available.
System time quality: BAD
I 1979-12-31 00:00:01.196 Network Interface 172.28.80.168 (255.255.252.0 ) : 00-03-2c-05-14-61
I 2018-07-19 14:21:06.263 Network Interface 172.29.80.168 (255.255.252.0 ) : 00-03-2c-05-14-62
I 2018-07-19 14:21:06.263 Network Interface 10.41.246.72 (255.255.255.0 ) : 00-03-2c-05-14-63
I 2018-07-19 14:21:06.265
I 2018-07-19 14:21:06.265
I 2018-07-19 14:21:06.266 Product : AC 800PEC PPE100/101
I 2018-07-19 14:21:06.266 Version : 5.1.0/0 (Build 5.1.48.40)
(XF801 integration version: 1.0-0)
I 2018-07-19 14:21:06.266 Created : 2016-12-16
NOTE : This is a BU IS specific firmware. Contact 'hotrollingmillsupport@se.abb.com' for XF801 related support.
I 2018-07-19 14:21:06.267 ABB AB
I 2018-07-19 14:21:06.267
I 2018-07-19 14:21:06.267 Controller Reset
I 2018-07-19 14:21:06.354 Position Module Firmware Name Date Version
I 2018-07-19 14:21:06.355 0 PEC800 FWPEC 2016-12-16 5.1.48.40
I 2018-07-19 14:21:06.355 OMEGA 2016-12-16 5.1.48.40
I 2018-07-19 14:21:06.356 PECIO omega driver 2005-04-13 2.00
I 2018-07-19 14:21:06.356 VICIdrvSim 2012-05-24 7.12
I 2018-07-19 14:21:06.357 CEX simulation N/A 0.0.0.1
I 2018-07-19 14:21:06.357 1 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 2018-07-19 14:21:06.358 FWCI854 PROG 3611540 A 2011-11-10 05.62
I 2018-07-19 14:21:06.358 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 2018-07-19 14:21:06.359 CI-Unit N/A CI854A PR:L
I 2018-07-19 14:21:06.359 2 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 2018-07-19 14:21:06.360 FWCI854 PROG 3611540 A 2011-11-10 05.62
I 2018-07-19 14:21:06.360 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 2018-07-19 14:21:06.361 CI-Unit N/A CI854A PR:J
I 2018-07-19 14:21:06.361 3 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 2018-07-19 14:21:06.362 FWCI854 PROG 3611540 A 2011-11-10 05.62
I 2018-07-19 14:21:06.362 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 2018-07-19 14:21:06.363 CI-Unit N/A CI854A PR:J
I 2018-07-19 14:21:06.363 4 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 2018-07-19 14:21:06.364 FWCI854 PROG 3611540 A 2011-11-10 05.62
I 2018-07-19 14:21:06.364 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 2018-07-19 14:21:06.365 CI-Unit N/A CI854A PR:L
I 2018-07-19 14:21:06.365
I 2018-07-19 14:21:06.366 Actual heapsize: 910708 kBytes, Available heap: 882387 kBytes
I 2018-07-19 14:21:06.384 RunMode
I 2018-07-19 14:21:06.388 License Manager: Feature Name Control_Software
I 2018-07-19 14:21:06.389 License Manager: Version 5.1.0
I 2018-07-19 14:21:06.389 License Manager: Hardware ID 00-00-00-00-00-00
I 2018-07-19 14:21:06.392 System Initialized.
W 2018-07-19 14:21:06.392 Unit= _SWFirmware 172.28.80.168 1040 BUM No conf image found on BUM
I 2018-07-19 14:21:16.394 Init Log Saved
I 2018-07-19 14:21:58.093 Create applications definition domain
I 2018-07-19 16:22:59.640 New time zone: W. Europe Daylight Time
I 2018-07-19 16:22:59.689 Create controller configuration domain
I 2018-07-19 16:23:01.530 AE System events to controller log: Medium Severity
W 2018-07-19 16:23:01.531 IP address change for ethernet port 1 will not take effect until controller reset
W 2018-07-19 16:23:01.532 IP address change for ethernet port 2 will not take effect until controller reset
I 2018-07-19 16:23:06.317 Protocol Handler Name = PhIPpin
I 2018-07-19 16:23:06.317 Version = 5.1.6.0 ; 2009-10-23
I 2018-07-19 16:23:06.318 Ph binary version = : 0x00000000
I 2018-07-19 16:23:06.318 Protocol Handler Name = PhIAC_MMS
I 2018-07-19 16:23:06.318 Version = 5.1.8.6 ; 2010-05-27
I 2018-07-19 16:23:06.319 Ph binary version = : 0x00000000
I 2018-07-19 16:23:06.319 Protocol Handler Name = PHModulebus
I 2018-07-19 16:23:06.320 Version = 5.1.46.301; 2010-03-17
I 2018-07-19 16:23:06.320 Ph binary version = : 0x00000000
I 2018-07-19 16:23:06.321 Protocol Handler Name = PhPECIO
I 2018-07-19 16:23:06.321 Version = 5.1.27.8 ; 2009-10-20
I 2018-07-19 16:23:06.321 Ph binary version = : 0x00000000
I 2018-07-19 16:23:06.322 Protocol Handler Name = PHCI854
I 2018-07-19 16:23:06.322 Version = 05.01-03 2010-03-04
I 2018-07-19 16:23:06.322 Ph binary version = : 0x00000000
I 2018-07-19 16:23:06.323 456 PhCI854 0 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.324 457 Ph Versions: 5 1 3 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.325 458 Ph Date: 7DA 3 4 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.326 404 WebserverGo variable access erro 0 FFFFFFE4 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.327 Protocol Handler Name = PHCI854
I 2018-07-19 16:23:06.327 Version = 05.01-03 2010-03-04
I 2018-07-19 16:23:06.327 Ph binary version = : 0x00000000
I 2018-07-19 16:23:06.328 456 PhCI854 0 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.329 457 Ph Versions: 5 1 3 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.330 458 Ph Date: 7DA 3 4 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.331 404 WebserverGo variable access erro 0 FFFFFFE4 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.332 Protocol Handler Name = PHCI854
I 2018-07-19 16:23:06.332 Version = 05.01-03 2010-03-04
I 2018-07-19 16:23:06.332 Ph binary version = : 0x00000000
I 2018-07-19 16:23:06.333 456 PhCI854 0 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.334 457 Ph Versions: 5 1 3 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.335 458 Ph Date: 7DA 3 4 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.336 404 WebserverGo variable access erro 0 FFFFFFE4 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.337 Protocol Handler Name = PHCI854
I 2018-07-19 16:23:06.337 Version = 05.01-03 2010-03-04
I 2018-07-19 16:23:06.338 Ph binary version = : 0x00000000
I 2018-07-19 16:23:06.338 456 PhCI854 0 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.339 457 Ph Versions: 5 1 3 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.340 458 Ph Date: 7DA 3 4 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.341 404 WebserverGo variable access erro 0 FFFFFFE4 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:06.344 PhIAC_MMS @ 0.5.1 Configure received 13 ULONG(s). ArraySize: 5
I 2018-07-19 16:23:06.344 CPhIAC_MMS::DoWork starting up
I 2018-07-19 16:23:06.345 Modulbus scan execution times is now restarted
I 2018-07-19 16:23:05.692 6356 config: PhResp. running... 1 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:05.693 6520 Created 1st driver 1 1 25D5E9C /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:05.705 1942 CPhCI854Base::Configure 1 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
E 2018-07-19 16:23:06.216 On Unit= 1.5 HWError CT0018 0000 See HWTree Error 16#00010001 16#00000001
E 2018-07-19 16:23:06.216 On Unit= 1.5.1 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:23:06.216 On Unit= 1.5.2 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
I 2018-07-19 16:23:07.465 2654 General: Config succeeded 1 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
I 2018-07-19 16:23:07.482 6356 config: PhResp. running... 2 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:07.483 6520 Created 1st driver 2 2 25D5EFC /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:07.488 1942 CPhCI854Base::Configure 2 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
I 2018-07-19 16:23:10.538 2654 General: Config succeeded 2 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
I 2018-07-19 16:23:10.546 6356 config: PhResp. running... 3 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:10.547 6520 Created 1st driver 3 3 219C72C /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:10.550 1942 CPhCI854Base::Configure 3 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
W 2018-07-19 16:23:12.768 A/E Burst: Prevented 35 alarms & events from being printed in the log, refer to an OPC AE client for more info.
I 2018-07-19 16:23:13.138 2654 General: Config succeeded 3 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
I 2018-07-19 16:23:13.148 6356 config: PhResp. running... 4 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:13.150 6520 Created 1st driver 4 4 1979BDC /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2018-07-19 16:23:13.162 1942 CPhCI854Base::Configure 4 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
E 2018-07-19 16:23:07.258 On Unit= 1.61 HWError CT0018 0000 See HWTree Error 16#00020001 16#00000008
E 2018-07-19 16:23:07.259 On Unit= 1.61.1 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:23:07.259 On Unit= 1.61.2 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
I 2018-07-19 16:23:14.697 2654 General: Config succeeded 4 0 0 /Builds/49/src/Platform/ControlIT/source/Profibus/PH/ProtocolHandler/Source/PhCI854/base/CI854ConfigBase.cpp
I 2018-07-19 16:23:14.741 New I/O-connections configuration.
I 2018-07-19 16:23:14.825 I/O-connections configuration waiting for application/s.
I 2018-07-19 16:23:15.380 Create application instance domain: R825915901Level1_Co18
W 2018-07-19 16:23:18.967 A/E Burst: Prevented 403 alarms & events from being printed in the log, refer to an OPC AE client for more info.
I 2018-07-19 16:23:22.897 Create application R825915901Level1_Co18
I 2018-07-19 16:23:23.760 I/O-connections configured.
I 2018-07-19 16:23:23.797 Start application R825915901Level1_Co18
I 2018-07-19 16:23:23.947 New time zone: W. Europe Standard Time
W 2018-07-19 16:23:24.544 A/E Burst: Prevented 61 alarms & events from being printed in the log, refer to an OPC AE client for more info.
E 2018-07-19 16:23:24.356 Unit= _SWFirmware CT0018 1010 Lost event notif to 172.28.80.22:22
E 2018-07-19 16:23:29.606 Unit= _SWFirmware CT0018 1010 Lost event notif to 172.28.80.22:22
E 2018-07-19 16:23:24.356 Unit= _SWFirmware CT0018 1010 Lost event notif to 172.28.80.21:22
W 2018-07-19 16:25:51.542 On Unit= 1.50.1 HWError CT0018 0000 See HWTree Error 16#00000010 16#00000000
W 2018-07-19 16:25:51.542 On Unit= 1.50.2 HWError CT0018 0000 See HWTree Error 16#00000010 16#00000000
W 2018-07-19 16:25:51.542 On Unit= 1.50.3 HWError CT0018 0000 See HWTree Error 16#00000010 16#00000000
W 2018-07-19 16:25:56.741 A/E Burst: Prevented 4 alarms & events from being printed in the log, refer to an OPC AE client for more info.
E 2018-07-19 16:25:57.986 Unit= 1.50 CT0018 0000 See HWTree Error 16#00000000 16#00000000
W 2018-07-19 16:25:57.986 On Unit= 1.50.1 HWError CT0018 0000 See HWTree Error 16#00000010 16#00000000
W 2018-07-19 16:25:57.986 On Unit= 1.50.2 HWError CT0018 0000 See HWTree Error 16#00000010 16#00000000
W 2018-07-19 16:26:03.386 A/E Burst: Prevented 1 alarms & events from being printed in the log, refer to an OPC AE client for more info.
E 2018-07-19 16:27:43.890 On Unit= 3.74 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:27:43.890 On Unit= 3.74.1 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:27:43.890 On Unit= 3.74.2 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
W 2018-07-19 16:27:48.960 A/E Burst: Prevented 81 alarms & events from being printed in the log, refer to an OPC AE client for more info.
E 2018-07-19 16:27:54.187 On Unit= 1.62 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:27:54.187 On Unit= 1.62.1 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:27:54.187 On Unit= 1.62.2 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
W 2018-07-19 16:27:59.309 A/E Burst: Prevented 79 alarms & events from being printed in the log, refer to an OPC AE client for more info.
E 2018-07-19 16:28:17.989 On Unit= 1.62 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:28:17.989 On Unit= 1.62 HWError CT0018 0000 See HWTree Error 16#00020001 16#00000008
E 2018-07-19 16:29:54.046 On Unit= 3.74 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:29:54.046 On Unit= 3.74.1 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:29:54.046 On Unit= 3.74.2 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
W 2018-07-19 16:29:59.118 A/E Burst: Prevented 64 alarms & events from being printed in the log, refer to an OPC AE client for more info.
W 2018-07-19 16:30:04.144 A/E Burst: Prevented 17 alarms & events from being printed in the log, refer to an OPC AE client for more info.
E 2018-07-19 16:30:34.919 On Unit= 3.74 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:30:34.919 On Unit= 3.74.1 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:30:34.919 On Unit= 3.74.2 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
W 2018-07-19 16:30:40.018 A/E Burst: Prevented 81 alarms & events from being printed in the log, refer to an OPC AE client for more info.
E 2018-07-19 16:31:09.353 On Unit= 3.75 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:31:09.353 On Unit= 3.75 HWError CT0018 0000 See HWTree Error 16#00020001 16#00000008
E 2018-07-19 16:31:09.666 On Unit= 3.77 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
W 2018-07-19 16:31:14.919 A/E Burst: Prevented 3 alarms & events from being printed in the log, refer to an OPC AE client for more info.
W 2018-07-19 16:33:42.550 On Unit= 0 HWError CT0018 0000 See HWTree Error 16#08020000 16#00000000
E 2018-07-19 16:34:30.051 On Unit= 3.74 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:34:30.051 On Unit= 3.74.1 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:34:30.051 On Unit= 3.74.2 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
W 2018-07-19 16:34:35.124 A/E Burst: Prevented 81 alarms & events from being printed in the log, refer to an OPC AE client for more info.
E 2018-07-19 16:34:50.802 On Unit= 3.75 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:34:50.802 On Unit= 3.75 HWError CT0018 0000 See HWTree Error 16#00020001 16#00000008
E 2018-07-19 16:34:51.724 On Unit= 3.76 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:34:51.724 On Unit= 3.76 HWError CT0018 0000 See HWTree Error 16#00020001 16#00000008
E 2018-07-19 16:36:03.503 On Unit= 3.74 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:36:03.503 On Unit= 3.74.1 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:36:03.503 On Unit= 3.74.2 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
W 2018-07-19 16:36:08.625 A/E Burst: Prevented 81 alarms & events from being printed in the log, refer to an OPC AE client for more info.
E 2018-07-19 16:36:27.353 On Unit= 1.60 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:36:27.353 On Unit= 1.60.1 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:36:27.353 On Unit= 1.60.2 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
W 2018-07-19 16:36:33.352 A/E Burst: Prevented 79 alarms & events from being printed in the log, refer to an OPC AE client for more info.
E 2018-07-19 16:36:32.103 On Unit= 3.75 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:36:32.103 On Unit= 3.75 HWError CT0018 0000 See HWTree Error 16#00020001 16#00000008
E 2018-07-19 16:36:33.953 On Unit= 3.77 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:36:33.953 On Unit= 3.77 HWError CT0018 0000 See HWTree Error 16#00020001 16#00000008
E 2018-07-19 16:36:54.403 On Unit= 1.63 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:36:54.403 On Unit= 1.63 HWError CT0018 0000 See HWTree Error 16#00020001 16#00000008
E 2018-07-19 16:37:33.778 On Unit= 1.60 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:37:33.778 On Unit= 1.60.1 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:37:33.778 On Unit= 1.60.2 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
W 2018-07-19 16:37:38.862 A/E Burst: Prevented 79 alarms & events from being printed in the log, refer to an OPC AE client for more info.
E 2018-07-19 16:37:59.205 On Unit= 1.61 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:37:59.205 On Unit= 1.61 HWError CT0018 0000 See HWTree Error 16#00020001 16#00000008
E 2018-07-19 16:38:01.055 On Unit= 1.62 HWError CT0018 0000 See HWTree Error 16#00000001 16#00000000
E 2018-07-19 16:38:01.055 On Unit= 1.62 HWError CT0018 0000 See HWTree Error 16#00020001 16#00000008
I 2018-07-19 17:05:01.652 Used MMS TCP-SendBuffers, Current: 0, Max: 2
I 2018-07-19 17:05:01.652 Used MMS TCP-RcvBuffers, Current: 6, Max: 12
<PRINTROUTINGTABLE>
I 2018-07-19 17:05:01.683 TCP/IP statistics
Controller has been running 0 days, 0 h, 0 m, 0 sec
File Descriptors:
Total: 150, Total in use: 35
Used by sockets: 31
Interfaces:
lo0 Link type:Local loopback Queue:none
inet 127.0.0.1 mask 255.255.255.255
UP RUNNING LOOPBACK MULTICAST
MTU:1500 metric:1 VR:0 ifindex:1
RX packets:5028 mcast:4890 errors:0 dropped:9
TX packets:5028 mcast:0 errors:0
collisions:0 unsupported proto:0
RX bytes:517k TX bytes:517k
motetsec0 Link type:Ethernet HWaddr 00:03:2c:05:14:61 Queue:none
capabilities: TXCSUM TX6CSUM VLAN_MTU
inet 172.28.80.168 mask 255.255.252.0 broadcast 172.28.83.255
UP RUNNING SIMPLEX BROADCAST MULTICAST
MTU:1500 metric:1 VR:0 ifindex:2
RX packets:431458 mcast:60372 errors:0 dropped:20
TX packets:307166 mcast:2448 errors:0
collisions:0 unsupported proto:0
RX bytes:218M TX bytes:199M
motetsec1 Link type:Ethernet HWaddr 00:03:2c:05:14:62 Queue:none
capabilities: TXCSUM TX6CSUM VLAN_MTU
inet 172.29.80.168 mask 255.255.252.0 broadcast 172.29.83.255
UP RUNNING SIMPLEX BROADCAST MULTICAST
MTU:1500 metric:1 VR:0 ifindex:3
RX packets:61103 mcast:60401 errors:0 dropped:0
TX packets:5278 mcast:2449 errors:0
collisions:0 unsupported proto:0
RX bytes:7176k TX bytes:1471k
motetsec2 Link type:Ethernet HWaddr 00:03:2c:05:14:63 Queue:none
capabilities: TXCSUM TX6CSUM VLAN_MTU
inet 10.41.246.72 mask 255.255.255.0 broadcast 10.41.246.255
UP SIMPLEX BROADCAST MULTICAST
MTU:1500 metric:1 VR:0 ifindex:4
RX packets:0 mcast:0 errors:0 dropped:0
TX packets:0 mcast:0 errors:0
collisions:0 unsupported proto:0
RX bytes:0 TX bytes:0
hostname inet address aliases
-------- ------------ -------
localhost 127.0.0.1
bootHost 192.168.1.1
vxTarget 10.41.246.72
gateway 0.0.0.0
Data buffers:
System buffers:
W 2018-07-19 17:05:01.688 TODO: VxWorks6.8 - statistics not complete
172.28.80.21 at 00:50:56:a7:4c:db on motetsec0
172.28.80.22 at 00:50:56:a7:80:4b on motetsec0
172.28.80.158 at 00:03:2c:00:2d:0e on motetsec0
TCP/IP Filter supervision:
UDP Always open ports:
UDP 147 Show remotesystem bursted: 0
UDP 2423 rnrp bursted: 0
UDP Source ports:
UDP Port: 2999 bursted: 0
UDP Port: 123 bursted: 0
UDP Port: 24230 bursted: 0
UDP Port: 2757 bursted: 0
UDP Port: 0 bursted: 0
UDP Destination ports:
UDP Port: 2999 bursted: 0
UDP Port: 123 bursted: 0
UDP Port: 3341 bursted: 0
UDP Port: 24230 bursted: 0
UDP Port: 2757 bursted: 0
UDP Port: 0 bursted: 0
</PRINTROUTINGTABLE>
by ahuerlimann Rank: 289 on 7/19/2018 10:33:33 PM | Like (0) | Report
Reboot was 16:22 .
by Stefan Stromqvist
Will dig further next week when I have returned from my vacation.
by ahuerlimann Rank: 289 on 7/31/2018 11:52:47 PM | Like (0) | Report
Hi Stefan. Interesting Story, it works again. I dont know whats is different...
by Stefan Stromqvist
Good to hear, but if you did not change anything I suspect the problem is still there and will return some day.
Suggest
1. Asking PEC support for advise
2. Document current controller log + "Network Information" data to have as a comparison baseline when/if the problem return
3. Document Ethernet statistics from the (hopefully managed) switch connecting the controller
4. Verify if switch management can ping the controller on primary/secondary port of controller (most managed switches have a "ping" tool built in)
Add new comment