AC800M : CPU stall timer has expired
this PM has been intentionally stopped.Reason: - CPU stall timer has expired (Acknowledged) - Manual shutdown was requested Press init button or remove power to restart...
Below is message coming in the backup controller , is this a know problem
800XA 5.1 REV E
AC800M PM866
FW866 2013-03-04 5.1.1110.3
Below is message coming in the backup controller , is this a know problem
800XA 5.1 REV E
AC800M PM866
FW866 2013-03-04 5.1.1110.3
Answers
Hello,
you should send the controller log file to your local ABB support center.
It can be a hardware issue, like bad grounding.
/Ronny
you should send the controller log file to your local ABB support center.
It can be a hardware issue, like bad grounding.
/Ronny
Hi you need to reset the first controller again by remove power supply or press INIT button less than 3 second
and then wait until complete restart and synchronization
Regards
and then wait until complete restart and synchronization
Regards
by Tejas.kareliya Rank: 344 on 4/21/2019 8:23:16 PM | Like (0) | Report
does this issue has resolution? I am also facing the same issue while changing over the Controller.