AC800M Profibus communication with Third Party DCS
I want to Profibus communication between redundant PM866 Controller using CI854A with Third party DCS. Both side will be the master so shall i use Profibus DP-DP coupler in between.
Also can the profibus communication be redundant & how will be the connection.
Rgds,
Naveen Garg
Also can the profibus communication be redundant & how will be the connection.
Rgds,
Naveen Garg
Answers
Greetings,
For Line Redundancy you have to use RLM or Ylink before DP/DP Coupler on AC800M side.
Hope it helps you.
For Line Redundancy you have to use RLM or Ylink before DP/DP Coupler on AC800M side.
Hope it helps you.