Profibus Communication with Third Party system
I want to do profibus communication with third party system. I am using redundant AC800M controller PM866 with CI854A.
Both side will be Profibus master so shall i use profibus DP-DP coupler in between CI854 & Third party.
Also Can Profibus communication be redundant, How will be the connection.
Rgds,
Naveen
Both side will be Profibus master so shall i use profibus DP-DP coupler in between CI854 & Third party.
Also Can Profibus communication be redundant, How will be the connection.
Rgds,
Naveen
Answers
Yes profibus DP DP coupler can be used. I have used Siemens DP DP coupler before, for redundancy you need two couplers one for each Profibus line.
Check https://forum-controlsystems.abb.com/... for additional info.