Alarm Disable / enable behaviour ?
I understand the need to use disable and enable of my alarms in my system. I do have an issue which I do not understand if I do the following workflow.
1. In my Alarm list -> Disable Alarm
The alarm becomes disabled, it also shows as MBL status
2. The Alarm I previously disable I enable it.
The Alarm dissapears of my list. If its in Alarm it becomes re-generated, if its not in Alarm I do not have any records of the alarm on my list anymore?
Can somebody explain me why I loose this Alarm? Why do I not still have it as an Event ? I do not understand why the Alarm just goes away, would appreciate any explanation of this issue. Thanks in advance.
Voted best answer
IIRC, a disabled alarm will not reappear if it goes inactive before enablement.
Events do not disappear unless being flushed out due to being last in FIFO queue.
Additional events can be enabled for enabling/disabling. Check Alarm Manager Special Configuration tab.
Events do not disappear unless being flushed out due to being last in FIFO queue.
Additional events can be enabled for enabling/disabling. Check Alarm Manager Special Configuration tab.
Answers
Ok the Alarm disappear from the Alarm List, like you have acknowledged it, but should be still in your event list. Or disappear it from the event list too?
/Erik
/Erik
When re-enabled if the alarm is acknowledged and then disabled, it will disappear from the list if the alarm is not active. If the alarm is active it will regenerate (start flashing again) on the list.
In 800xA all alarms are events, it should be there in the event list, try removing all the filters from the event list ( select all event categories) and then check.
In 800xA all alarms are events, it should be there in the event list, try removing all the filters from the event list ( select all event categories) and then check.