Third party opc
Dear team,I am using Compact Him with our PM 583 PLC.Now communication with PLC and scada on plc-opc and its working fine.Now I want to connect Third party opc (B&R plc) want to communicate with our compact hmi. B&R opc is in build in Its plc system.Now I am getting the b&r PLC opc data on abb opc testing tool. But when I configuration in compact him , there is not showing this data.....So what we have to check for this so I can get the data....And one more thing shall I need to change in DCOM setting? When I check in Service Structure , Opc-Da....Service status is showing Undefined....Start Time ;Zero time..Regards,Chandraprakash
Answers
Check your DCOM settings.
Asynchronous DCOM across different domain/workgroup may require additional user accounts for you to be able to define permission on each stage.
In asynchronous DCOM, the server will call back to the client.I seem unable to attach a PDF document I have with an example. Please search older threads, I have used it frequently here on AKS.
Asynchronous DCOM across different domain/workgroup may require additional user accounts for you to be able to define permission on each stage.
In asynchronous DCOM, the server will call back to the client.I seem unable to attach a PDF document I have with an example. Please search older threads, I have used it frequently here on AKS.