Modbus TCP error code -7006 between CI867 and Unitrol AVR
Hi all
I have a problem with Modbus TCP communication between an Unitrol AVR and a CI867 card. The connection to the Unitrol itself is ok (MBTCPConnect block receives valid signal back), but when I try to read some holding registers (%QW10#100), the MBTCPRead block shows the error code -7006.
In order to troubleshoot the problem, I've tried to read the values from the Unitrol with a Modbus master installed on my PC (ModScan). From this tool I can read the values without errors. Furthermore I have simulated the Unitrol, by attaching my computer with a Modbus slave (ModSim) installed. The CI867 was able to see the values from this slave without any errors.
In order to give you some more information, I've attached a pdf file with screendumps.
The Modbus slave device ID is 64.
I'm trying to read holding register 40101 and 40102
IP-address for Unitrol is 172.16.80.105
If more information is needed, please don't hesitate to write it, and thank you very much for your answers in advance.
Best Regards
Matthias
Answers
Try with "Default diagnostic poll time for serial slaves" = 0 In Settings for CI867.