Hi dear all, I have installed ABB Engineering Studio 6.0.0-2, some library objects can not be inserted to the function designer without any message! While this can be done in the diagram of the control builder envirement!
for example objects from ProcessObjExtLib 2.6-3 like MotorUniM:
Object Types\Control System\AC 800M/C Connect\Libraries\ProcessObjExtLib x.x-x\Control Module Types\MotorUniM
Answers
Does MotorUniM have a Function aspect on it in the Object Type Structure?
I believe, the function aspect is not available for this CMT. But as you have already installed Engineering Studio, you should be able to add an aspect named 'Function' on this object in object type structure >> Libraries >> ProcessObjExtLib >> MotorUniM.
After adding this function, you should be able to drag and drop the object in Function Designer.
For a library object to be placed in the function diagram, it should have a Function aspect. So, for user defined libraries, user needs to manually add a Function aspect for the library object to be readable by function diagram.