Excel report using Freelance
I am trying to create a Excel report in Freelance, but I don´t know the necessary steps to create them. I checked the help installed but it is not enough. I would like to knoe where can I get a tutorial, video or help.
I am a new user, for this reason there are many basic things that could be omiting.
Thnaks for your help.
Voted best answer
Hi orguti,
The creation of Excel Report is described in detail in Freelance Manual 3BDD012518 (Engineering Manual - Operator Station Configuration) in Section 4: Logs. To create a Report you need to create a template in Excel (use Define Template button on General tab of Parameters window). Use this command:
<Get Value(VAR,NEXT)>
in the first cell of the area where you want to get the values, where VAR should be replaced with variable name and NEXT can be any of: NEXT_DOWN, NEXT_UP, NEXT_RIGHT, NEXT_LEFT and shows where next value will be put in.
Also remember to set values in the Filing group of General tab of Parameters window. These parameters tell you when a report will be started and how many values with what cycle time will be gatherth.
Please consult the Manual for details.
Hope this helps,
Mike
by orguti Rank: 1957 on 6/8/2018 10:29:42 AM | Like (0) | Report
Thanks for your answer Mike. The information has been very useful and now I am creating excel reports.
Add new comment