How can I read OPC AE messages from Third Party OPC Server into System 800xA?
Hi everyone,
Please, how can I request and read OPC AE messages from Third Party OPC AE Server to System 800xA? (I'm working at System 800xA 6.0.3).
Are there any document with tips?
Thanks for attention.
Voted best answer
Hi,
You can refer manual System 800xA 6.0 Configuration (3BDS011222-600)
Page 537 onwards for Third party AE server configuration into 800xA
Hope that helps
Answers
You can refer Manual 3BDS011222-600.
Integration can be possible with 3rd Party OPC AE Server. Follow the steps
1. Create Evenet Collector Service Provide
2. Create Collection Definition
3. Perform Category Upload
(A) Selecting Priority Mappings
(B) Selecting Category Mappings
4. Source Object Interceptor(Optional Step)
5. Adding Translations (Optional Step)
6. Setting up a Redundant Server (Optional Step)
Most things are covered in the document. Event to Object relation is by name, if no object with the same name is found then a dummy object in the lost+found will be created.
If your events have different names you may try the "controller name" aspect to map them to the desired object.
/Erik