Freelance 9.2SP1 -Foundation Fieldbus
Hi
In one of the project I am facing problem in getting the reading of FF instruments in Freelance system at two sites.
1st Site.
I have one Level Transmitter of VEGA Grieshaber KG. The Model No is VEGAPULS 62 and Device Revision is 2.21, Capability file Version 1.7. I am not able to assign it in FF LD800HSE H1 Port segment. In the same segment the other make devices are getting assigned(other than LT). Though with the same settings at another location its getting assigned. Please tell me what may be the reason for not happening at this location.
2nd Site.
I have one ABB make Pressure transmitter Model 266 P-dP, Device Model 01.00.00, Capability File Version is 1.8. Initially I was able to assign it and I was getting data in Freelance system. After few Months the data stops coming. When I checked , The device was ON in Field and showing values, but it is not coming in Live List of Particular H1 Segment.
Please tell me the solution for both of above.
Answers
another possibility is adress range, try to change adress manually using one handheld
by himanshu Rank: 249 on 8/25/2015 6:43:27 AM | Like (0) | Report
There is a rotory switch on the top of transmitter, it was set at 1. I changed it to 0 and then re-configured the LT again, After that tried to assign it, and now its communicating with the system