Alarm setting in Control Module!!!
Hi,
I’ve never used before control module. I used FBD.
I think this is a problem below
PS21_PC1_1 is a program AIS1, using control module and I made in program AIS2.
So, I have two AIS1 and AIS2.
However, AIS1 in control module only can not showing up alarm at all.
Do I have to setting for control module to get alarm??
Plz, give some help ASAP.
Thanks.
Answers
When online with control application, right click AIS module and select "Alarm conditions". Compare AIS1 with AIS2.
Cond state 0 often mean error in configuration of alarm, eg uniqueness of name & condition not met or invalid parameter, eg severity or priority = 0.
Cond states are listed in CBM OnLine Help, search for Acknowledgement Rule.
If cond state is 3, 4 or 5 an alarm is raised from controller application (=problem is upwards in system).
Add new comment