IO allocation of 3_part profibus slave with Function Desginer
After import of gse (siemens DP/SP coupler) file to system and mapping och input/output data to real and bool data types i ABB.
In function desginer it is possible to use io allocation tool to allocate cbm_dis, cbm_dos, cbm_ais ..... to the imported hardware.
BUT, functions designer always shows that io is not allocate due to the fact that it is!
If i use for eg. an s800 io it shows the correct status of io allocation.
Not a big problem but it would be nice to know what is missing.
With regards Staffan
Answers
Hi,
After importing GSD file,go to object type structure ->control system->hardware library you can able to see the extracted GSD file add an aspect function designer in that so that you can able to do IO allocation as same as S800 IO in FuD.