Hello,
I have a SmartClient who uses 800xA trend browser to show signal trends, the problem is the SmartClient trend doesn't shows the signal unit.
We are using the level2cc object, the signal used is "in.forward.value" where the unit is in "in.forward.range.unit".
if a SmartClient trend is saved, Is possible to set manually the unit but I don't want to have an independent configuration for trend in 800xA and SmartClient.
Thanks in advance.
Voted best answer
You need to use "Object configuration tool" for Unit configuration also and you need to check where the value had been configured for the query type in (object configuration tool->level2cc object type) and then configure the unit based on the query type where value is configured
Answers
You need to use "Object configuration tool" for unit configuration, This should be done in SC server. You need to configure unit where "value" had been configured for query type from object type "level2cc"
I have attached a short example of how changes are made utilizing the Object Type Configuration Tool in Smart Client. This example is based on adding parameters for Softpoint Objects, however, this procedure applies to other Object Types also.
Regards,
Geof Ledin