acs800 actual time
hi every one and thanks
in the morning when i pressed the arrows to see the last fault , i saw
+1 last fault
over current
48573 h 51 m 23 s
how can calculate to reach the actual time which that fault had occurred in the last night.
best regards
Answers
Hi
the drive indicates for the fault, how much time has elapsed since it was switched on at the fault event occurred.
This is sure not a good indication about the precise hour when the drive give the fault.
Hope this help you
From this we can not able to reach actual time.
If additional modules added and current time is set then only we can match with actual time.
Otherwise we can see last faults only
If additional modules added and current time is set then only we can match with actual time.
Otherwise we can see last faults only
by mohsen1354 Rank: 2635 on 6/2/2018 2:28:50 AM | Like (0) | Report
thank-you
but i think that indicates how much time has elapsed since the power has been on for first time .
is there any parameter to set to register the actual time of the faults .
i appreciate your help
Add new comment